Been doing some searching and see that this Hager rcd which is the same spec as the mk on fitted has the neutral on the right which would save a whole load of pain of switching it to the other end of the cu.
80 Amp 30mA RCCB RCD Double Pole Trip Switch Circuit Breaker 80A Hager CD280W 3250611645085 | eBay - https://www.ebay.co.uk/itm/80-Amp-30mA-RCCB-RCD-Double-Pole-Trip-Switch-Circuit-Breaker-80A-Hager-CD280W/301759392855?epid=1826248222&hash=item464242ec57:g:E0IAAOSwetxa6d~N
It’s states it a standard din fitting. Can anyone confirm if it will fit the sentry cu? Does a swap to this sound like a sensible and ok solution?
My last post is still only theory until an electrician makes the re-arrangement and you see how everything operates. I stand by my initial recommendation of dividing up the final circuits over 2 or more RCDs/RCBOs and introducing some spare ways at the same time. You run at risk of nuisance tripping by protecting all final circuits by one RCD because of accumulated earth leakage eating into the residual current trip level of 30mA.
I looked to see if you have any electrician's qualification but nothing was posted. Assuming you are not it is time to employ one - if I am wrong then forgive me. EF members can advise you on someone local to you who 'cuts the mustard' and will give you some options and prices.
Yes, I think unusual electrical disturbances may have caused trips and the effects of some mains disturbances may be exacerbated by accumulated earth leakage and only having the one RCD.
Geoff ,a BG 80a/30ma RCD is arranged with the neutral on the right, they are also reasonably priced and I've never had an issue with them. However this is just for information as I'm not condoning fitting different makes of device in a CU, the regs frown upon it. :eek::rolleyes:
Ah thanks. I just saw this after I posted the reply about the Hager one too. I might have a look at this too. Sounds like a simple solution. I still cant work out what the prob is with a correctly fitting and Proper specced module in a different case is but there you go. Thanks
Reactions: Dave OCD
I agree Geoff, the only thing to watch out for is that the outgoing busbar and neutral connections line up nicely without having to force anything - some devices have the cage clamps arranged at different depths in relation to the din rail. And this isn't a new installation, could well be a maintenance job. :)
Thanks, yes noted. I just like to have a bit of an idea about the options and potential solutions before I engage someone. Thanks for all your help everyone.
I only fit RCBO boards, resolves all the nusiance tripping issues - acculimative normal internal leakages & external supply fluctuations. The Lewden boards are very resonably priced.
In my experience it's most unlikely to be a faulty RCD.... hardly ever happens.
RCDs trip when some of the neutral current flows in the earth conductor. So
Cumulative leakages of all the combined neutrals downstream from that
RCDs trip when some of the neutral current flows in the earth conductor. Remember these suckers trip when the leakage current is the size of a gnats dick.......So
1 Cumulative leakages of all the combined neutrals downstream from that RCD. are you able to split some circuits to an additional RCD?
2 excessive leakage on one of the circuits. look at anything with an element that might have absorbed moisture OR a water leak that has got into a termination somewhere. OR even the end of a cable that's unterminated that gets moisture across neutral and earth
3 out in the house somewhere is there a neutral that's either crossed over with another RCD ie phase on one RCD neutral on another or shared onto another RCD. These things can happen at renovation time.
Just had a look at the photo. FAAAAR too much cumulative leakage will be the issue. Upgrade the board. Swap all the MCBs for RCBOs on each circuit. that'll sort it
Best of luck
  • Informative
Reactions: Bul and marconi
Hi - just looking at the innards of your board - I think it's time for it to be retired. Several reasons, but "quart in a pint bottle" comes to mind :) .
Yes, the consumer unit is obsolete and any new parts if available will be some years old now. The connection to MCB 4 is rather poor, and the large neutral wire is likely to be a poor fit in the small terminal 12. It would be a waste spending money on this old unit, it has already been modified more than once.
So for those following this exciting thread who like a happy ending....(!)
Managed to get a local spark out this morning. Ran the circuit tests - all ok.
Swapped the rcd for a BG one which has the L N connections on the opposite sides.
Rcd reset first time with all MCBs on! Result!
I’ll look at the options for a new CU with a bit more space in the new year.
So I think Marconi wins the prize for spotting the wrong handed rcd. Cheers!
Thanks to everyone who contributed and helped move the thinking on. At least you got to find out the ending!
Great stuff. Thanks for letting us know.
Reactions: Dave OCD
Hi - I might be the only person that didn't quite understand the wrong handed rcd. Could anyone explain it again or do a line drawing. I might be slow but I'm honest and interested.
If you look back at my pic of the CU you'll see the RCD is mounted on the right hand side of the CU. The live is therefore goes on the left of the RCD as this has to connect to the live bus and the neutral goes on the right. In my case the RCD had been replaced with a more recent model to that originally fitted. The newer CU's (which this was designed for mount the RCD at the left hand end). These therefore need need the RCD designed to have the live on the right hand side to connect to the live bus and the neutral on the left.
As my old style one had been replace with a new style one without the person realising the difference it meant that the RCD had it's live and neutrals reversed which was causing the tripping problem when trying to reset it. The house supply was not reversed - just the RCD. Hope this makes more sense. No problems since!
Haven't read the full thread but always reset the board with all breakers in the off position then turn them on one by one as certain circuits may have a high load connected to them,, think PC's firing up as on auto reboot etc etc.
Good practice.
Totally understand now - Thanks Geoff. This has been an extremely interesting thread and really shows the forum at it's best.
Can't reset the RCD with any MCB's on - Faulty RCD?
Geoff101,
Bul,