Just getting ready to wire up this 100 amp subpanel., The subpanel is being fed from the meter base, not the main panel in the house. It doesn't look to me like the feed coming in at the meter base is bonded. I know we don't normally bond a subpanel because the main panel is normally bonded. So should I go ahead and bond it and If I do bond this subpanel, will I need to add grounding rods or can I just run grounds from subpanel to the ones already at the meter that were installed by the electric company? I've included a couple more pics of the meter base I will be coming from. The 30 amp breaker will move to the sub as they will be in the same room. Looks like the neutral bar is going to be fun trying to connect #3 gauge wire to...
box1.jpg
box2.jpg
 
Just getting ready to wire up this 100 amp subpanel., The subpanel is being fed from the meter base, not the main panel in the house. It doesn't look to me like the feed coming in at the meter base is bonded. I know we don't normally bond a subpanel because the main panel is normally bonded. So should I go ahead and bond it and If I do bond this subpanel, will I need to add grounding rods or can I just run grounds from subpanel to the ones already at the meter that were installed by the electric company? I've included a couple more pics of the meter base I will be coming from. The 30 amp breaker will move to the sub as they will be in the same room. Looks like the neutral bar is going to be fun trying to connect #3 gauge wire to...
View attachment 101453View attachment 101454
The code on adding a sub panel needs 4 wires to it and you will have to install a ground bar. Yes the neutrals needs to be separated from the equipment grounds. It’s best to get a main lug only panel. No ground rods are required and your main panel has been bonded, if not you would have eradicate voltage
 
The code on adding a sub panel needs 4 wires to it and you will have to install a ground bar. Yes the neutrals needs to be separated from the equipment grounds. It’s best to get a main lug only panel. No ground rods are required and your main panel has been bonded, if not you would have eradicate voltage
Thank You, I have installed the ground bar already and do have a main lug only sub which will only have 4 breakers in it. I have 4 individual #3 TNNH wires that I am planning to run to the shop with sch 40, nothing going underground or wet location, it's only a 2 foot run from meter to the house
 
Thank You, I have installed the ground bar already and do have a main lug only sub which will only have 4 breakers in it. I have 4 individual #3 TNNH wires that I am planning to run to the shop with sch 40, nothing going underground or wet location, it's only a 2 foot run from meter to the house
Sounds like you have it under control but please disconnect the wire to the ground rod you installed at your sub panel it is not required
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
florida
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United States of America
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
Do I Need To Bond My Subpanel?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
3
Unsolved
--

Advert

Thread statistics

Created
Inky86,
Last reply from
Megawatt,
Replies
3
Views
1,558

Advert

Back
Top