Greetings,

I'm a EE and have installed many electrical systems but am now dealing with my first large 3PH install on our property. I'm not formally trained in this area but very familiar as a EE. Anyway, can someone help me with proper neutral wire sizing?

I've done a bunch of research and am finding mixed answers. It comes down to this:

I'm planning on running 1000 MCM aluminum underground from a main disconnect at the pole to a MLO panel at our building about 400 feet away. This is for a 480V Wye Configuration with 400A meter.

I know the safe bet is to use a 1000 MCM for the neutral. But how do I go about proper sizing? I could save quite a bit of money if I'm allowed to run a smaller gauge wire for the neutral.
 
Greetings,

I'm a EE and have installed many electrical systems but am now dealing with my first large 3PH install on our property. I'm not formally trained in this area but very familiar as a EE. Anyway, can someone help me with proper neutral wire sizing?

I've done a bunch of research and am finding mixed answers. It comes down to this:

I'm planning on running 1000 MCM aluminum underground from a main disconnect at the pole to a MLO panel at our building about 400 feet away. This is for a 480V Wye Configuration with 400A meter.

I know the safe bet is to use a 1000 MCM for the neutral. But how do I go about proper sizing? I could save quite a bit of money if I'm allowed to run a smaller gauge wire for the neutral.
A good rule is size it at 83% of the 400 amp panel for a single family dwelling. So size it for 383 amps
 
A good rule is size it at 83% of the 400 amp panel for a single family dwelling. So size it for 383 amps
I’m sorry it’s 332 amps
 
Greetings,

I'm a EE and have installed many electrical systems but am now dealing with my first large 3PH install on our property. I'm not formally trained in this area but very familiar as a EE. Anyway, can someone help me with proper neutral wire sizing?

I've done a bunch of research and am finding mixed answers. It comes down to this:

I'm planning on running 1000 MCM aluminum underground from a main disconnect at the pole to a MLO panel at our building about 400 feet away. This is for a 480V Wye Configuration with 400A meter.

I know the safe bet is to use a 1000 MCM for the neutral. But how do I go about proper sizing? I could save quite a bit of money if I'm allowed to run a smaller gauge wire for the neutral.
I also need to ask, is your building going to be used as a commercial building. If so you are not allowed to derate the neutral.
 
  • Informative
Reactions: pc1966
Apart from any regs that apply in your location, you need to understand the loads.
At one extreme, if all loads have non-complex waveforms then there's scope to reduce the neutral. At the other extreme, you could need a neutral larger than the phase conductors as third harmonics add rather than cancelling. Things like computer power supplies have got a lot better (for regs compliance) over the years, but flouros with magnetic have a very peaky current waveform.
 
  • Like
Reactions: pc1966 and Megawatt

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Texas
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United States of America
What type of forum member are you?
Electrical Enthusiast (Unqualified Hobbyist etc)
Business Name
Texas Urban Sawmill

Thread Information

Title
480V 3PH Neutral Wire Sizing
Prefix
N/A
Forum
Commercial Electrical Advice
Start date
Last reply date
Replies
4

Advert

Thread statistics

Created
dcg4403,
Last reply from
Simon47,
Replies
4
Views
1,309

Advert