S
Simon81
HiCan anyone help me with regards to filling in a niceic part p cert with regards to the part were it concerns tt.This is on page 2 I need help with the parts electrode resistance ra , is this the measured ze result I have taken ?And also method of measurement ? Also what is the maximum ze for a tt system , I no it's 0.35 for tncs and 0.80 for tns. Any help is appreciated Thanks
i would just get the Ze. a TT system can be almost anything, but the brb says anything over 200ohms can be unstable. niceic say 100ohms. there is no stipulated maximum as even with 23ohms, your fault current would only be 10A, so RCD is used to achieve disconnection times. max. value of Zs is then entered as 1667ohms.
Ra & Ze are essentially one and the same in that they are the resistance of the earth electrode & the main earthing conductor connected to it..
Method of measurement would either be a proprietory earth electrode tester with spike kit (prop test) or using an earth fault loop impedance tester (EFLI tester). The bracketed wording is what I put in the boxes obviously depending on which method is used.
BS 7671 states that the maximum measured Ra/Ze on a TT system should not exceed 200ohms, whilst the NICEIC require no more than 100ohms.
GN3 has a diagram on on both methods plus other info.
Snap......
Ra reading can be taken using meathod 2 by an earth loop impedance tester
the max reading is in theory 1667 ohms but you should try to get bellow 200 to allow for sesioal changes
Thanks formal your replys got a ze of 4.69 just had a nightmare with it all. Also I have been told to enter 0.2 in the disconnection time and have been given the following maximum zs for the following mcb 6amp 38.3316amp 14.3820 amp 11.5032amp 7.19Does anyone no if this is right?
Oh dear.....you need to take the 2391.
So do you no the right answer wirepuller or do you just leave smart arsed comments to try and look like you do. I no electricians who got every qualification you can name but when it comes to tt systems they haven't got a clue !!!
Absolutely, are you installing work as a competent person?
I'm all for helping here but your questions are certainly not inspiring any confidence whatsoever in your ability to install, test and certificate a TT system!
Apologies for being blunt but given your questions I would not want you testing my installation.....anyone testing and filling in a cert should not have to ask.
If you are learning testing and your questions relate to a hypothetical installation fair enough,I apologise.
If you are testing an actual installation for someone you shouldnt have to ask questions like this.
I have never worked on a tt system that all and I don't no any other person who has ,
But why didn't you read up on the requirements for TT before getting involved in someone's installation?
I've got some sympathy for the OP here.
The OSG defines limitations for TNCS and TNS very well but when it comes to TT is less than clear having 200 ohms or 100 ohms for the Re/Ra doesn't help. When it comes to main bonding its the same ambiguity.
Lets hope such "details" are clearer when the next edition of the OSG comes out.
For what its worth I'm with the NICEIC to aim for sub 100 ohms, and I'd like to see main bonding brought into line with TNCS and TNS too.
Tin hat on!
I dont think its unreasonable to expect an electrician to have an understanding of most of the requirements of a TT, even if they come upon them only occasionally
Once again Simon I apologise for the tone of my post,although I stand by the gist of what I was trying to say.
At least you have asked for the correct information,rather than fabricating a cert in the pub which is what a lot of blokes would do if they didnt know....(and even if they do know)
trhe bit in red is gibberish. ok.?
Tin hat on!
But look what he posted above regarding maximums for devices, that was just a lack of basic knowledge, never mind TT specifics!
I've got no sympathy whatsoever, he could be installing this at my mother's house!
How can we all bang on about competency and sliding standards then defend posts like this one?
If the post had started "I'm doing a TT system next week, I have a few questions.......
Reactions: 2 people