This is a question I have to admit I don't know the answer to, hard to believe I know! What is the period after which test equipment needs re- calibrating? As far as I know it is yearly, but I could be wrong. I ask because the dno I worked for had an engineer who built a test rig. The idea was that as there were about a thousand items of test gear used at our depot, it would be more economical to do it in house. So every year a dedicated set of test instruments were sent off to be calibrated. They were then used as 'masters' to be compared to via the test rig. Some items weren't tested, such as pulse echos, sniffers, cat and Genny etc, which either worked or didn't, same with Fusemate and Rezap portable circuit breakers. We were able to test AC and DC current and voltage earth / neutral loop impedance, impedance and afew other tests like phase rotation, test lamps etc. What do others think of this method? Any items found to be outside the limits were sent away for recallibration or scrapped. I think the only test gear not tested was the RCD tester, which we didn't use anyway. I would like to hear opinions on this, for once it doesn't concern me!
 
I can't on the face of it see a problem, the gear was also checked for damage, condition and batteries cganged etc. and this is a dno.
 
I bi-annually calibrate about 30 of these,

Seaward Clare Hal 104

001.jpg


I have a Clare v242 calibration unit to do this.

42657_2112558.jpg


Every day I check the Hal testers with a Y160

19-Fault-Simulator-[Y160H]-2.jpg


But I still send my fluke meters away to be calibrated once a year by RS Components

The V242 and Y160 are also calibrated by RS Components
 
I believe the minimum is a yearly calibration and a certificate of calibration.
If your kit isn't certified, any testing you do with them can be voided.
Test sheets ask for the serial number and make of your equipment. There must be a register of calibrated equipment.
 
That sounds about right. When we tested them the serial no. make and results were recorded, but of course most of the time they were used the readings were not recorded, as they weren't required to be.
 
reminds me of the old story about the factory hooter in the town. Every day the guy set his watch by the big clock in the watchmakers' window on the way to work to make sure it's spot on, then set off the hooter 8am.
Then one day his watch was on the blink so he took it in to the watch place on the way to get it repaired. Went to pick it up, and checked it against the big clock in the window, job's a goodun.
Then the shopkeeper told him "I know that clock's spot on, I adjust it every day when the factory hooter goes off"
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Cumbria
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Retired Electrician

Thread Information

Title
Test equipment certification.
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
10
Unsolved
--

Advert

Thread statistics

Created
Percyprod,
Last reply from
MDJ,
Replies
10
Views
2,810

Advert

Back
Top