I had a solar panel system fitted 22 Feb 2012. The system includes a 15 panel sharp 245 array split into 2 strings of 9 and 6 running into a Sunny Boy 4000TL.

They system seems to produce consistently until about midday then cut out for periods if there is a decent amount of sunlight. I have been monitoring the system with Sunny Boy Explorer and noticed if the combined string voltages exceed 500v then the output drops to 0A and 0W. This remains the case until the voltage drops below 500v.
When running normally the volatges for each string are 280-290V and 170-180V. This can then jump to over 300V and 200V and knock the system out. I believe the inverter operates up to 550V. Would changing the inverter to the 4000TL with Reactive Power Control which has a 750V limit cure the problem or is there a more fundamental issue here.
I have also noticed recently that output power has sometimes been exceeding 4.2KWh which seems strange for a system with a stated output of 3.675KWh.
The installers have been around a couple of times and seem a little mystified but have suggested replacing the inverter as a first solution.
If anyone can offer me some advice I would be most grateful.
Cheers
Motters
 
Hi
The only fault I have seen is on the software as Grid Fault(1) and this seems to switch from an incoming fault to an output fault.
Thanks for your reply.
Cheers
Motters
 
I don't see the setup as being a problem. Looks fine to me with those voltages.

Grid fault does sound more likely to be the problem.

Is your installation in a rural area? Is your install far away from the electricity meters?

I supect that you are having issues with high voltages - caused by high grid voltage or voltage drop. Or it could be that your inverter isn't set up to G83 - although that seems unlikely if your installers have already been out twice already.
 
Hi
Thanks for your reply. Yes I am in a rural area and the run from the inverter to the meter is about 10m.
Voltage in this area is about 242v nominally.
Is there a reason why the system is fine up until about midday ??
Is there a realistic solution to this problem, will changing the inverter sort it out ?
Not an electrician by ant standards, my understanding goes about as far as A level physics and that was quite a few years ago. LOL.
Thanks again for your reply.
Cheers

Motters
 
The grid voltage can sometimes peak around midday so this tends to be the time when it would kick out - particularly if there are other installs in the area that are exacerbating the problem.

10m should be fine for the cable run to the inverter, as long as the cable size is big enough - should be at least 4mm2, possibly as much as 6mm.

From the info you have given, I'd be surprised if the problem was the inverter and therefore changing it, in my opinion, would not help solve the problem.
 
The grid voltage can sometimes peak around midday so this tends to be the time when it would kick out - particularly if there are other installs in the area that are exacerbating the problem.

Yes, grid voltage in my neighbourhood was typically 238-242V, but now that sunnier weather is here (and there has been a bit of an outbreak of PV locally), the grid voltage often runs at 245-250 on sunny days.
 
Hi
Thanks again for your replies. Is there a solution to this or do I just have to live with it?
I wondered if FB had had any problems similar to mine as the voltage in that area seems similar.
Thanks again
Cheers
Motters
 
Hi
Thanks again for your replies. Is there a solution to this or do I just have to live with it?
I wondered if FB had had any problems similar to mine as the voltage in that area seems similar.
Thanks again
Cheers
Motters

No problems at all with my system.
I work from home so if I'd be more likely to notice a problem than most people.
I have an Aurora PVI-3600-UK and the manual says that it operates at grid voltages in the 211 to 264V range.
 
Does the grid fault error message coincide with the power drops, or is it just at dawn and dusk? My inverter sometimes flashes its error lights briefly at startup and shutdown.

I didn't notice you mention whether you panels have anything at all possibly shading them around the time of their power drops. This is well-known and has been a much-discussed issue on here.
 
ive looked on sunny design and a 4000tl20 is fine to have with your system
sma technical helpline is the best people to ask as they made it 01908 487569 or 01908 304850
 
im assuming you have a TT earthing arrangement the ac cable installed cannot exceed 1ohm as sma state. this could be the problem
 
Hi
No shading issues and its difficult to be absolutely sure if the faults occur at the exact moment it cuts out.
The inverter Output Voltage range is 180-280V AC and can be adjusted to suit different countries. How does this affected or cause the input voltage to jump to over 500V.
Getting a bit out of my depth here.
Cheers
Motters
 
Hi Sedgy thanks for your reply. Cable is 4mm so I have been advised is suitable for the job. Not sure about the earthin.
Thanks Motters
 
Hi
No shading issues and its difficult to be absolutely sure if the faults occur at the exact moment it cuts out.
The inverter Output Voltage range is 180-280V AC and can be adjusted to suit different countries. How does this affected or cause the input voltage to jump to over 500V.
Getting a bit out of my depth here.
Cheers
Motters

The input voltage that you are talking about is the DC side of the inverter - this voltage does not affect the voltage on the AC side.

High impedance could be the problem and this may mean that you'd need to install a different model of inverter.

What has your electrician said about it? Has he ruled out any of the possible issues that we have suggested?
 
Could this be the same problem that sanyo/SMA had?
If the system is split on two strings, is it possible that just as the sun is coming around the inverter is searching the wrong power curve, maybe switching the optitrac on would cure it?
Just a thought.
 
I don't think this is a Sanyo/SMA compatibility issue as there are grid fault error messages. I would also doubt that the cable size is the issue.
 
Another suggestion then, put 2x24hr voltage monitors one on the incoming and one at the inverter, this will then show you what it is really happening and give you some accurate data to work with.
I am aware that the DNO have such a system, not sure where you can obtain them from though.
In my opinion it is normally an installation/design problem rather than the grid, but never say never.
Just another thought.
 
I have found if more than one install is on the same line the the wire size does matter, I do not know the reason why this is, however we had an install of 2 x 3kw systems ground mount 15meters away from house, both properties were tripping, one was on other was off scenario. we changed the wire from 4mm to 10mm after DNO said no problems on grid.

After changing the wire both systems have worked perfectly well, the 10mm was a bit overkill but I do beleive there is a fundimental problem with feedback to inverters in close proximity, however that would not really explain how changing the wire size would help.
 
Hi
Thanks everyone for your replies. There would seem to be no obvious solution and I`m out of my depth.
I just cant understand why the system seems to work fine until midday and then the input voltage jumps to over 500V DC, knocks the system off and then its on and off for the rest of the day.
Thanks again everyone
Cheers
Motters
 
the voltage of the 2 strings is independent, you don't add them up when looking at the voltage limits.

I reckon you've got 2 issues going on here...

1 - System is running higher than it's rated capacity, so self limits by adjusting the voltage to a less efficient point on the voltage curve, which is why you're getting such odd voltage readings.

2 - At the same time, you're also trying to push too much power down too small a pipe, resulting in the AC voltage from the inverter going up significantly, probably past the 253 10 minute average limit. I'm almost certain it should be 6mm cable on the 4000TL for a 10m length precisely to stop this happening.

Suggest to your installer that they try swapping out the cable before swapping the inverter.
 
I agree i think at its peak at that particular time its knocking it out
u should change ac cable it will be cheaper also you should phone Sma first as the inverter might need tweaking on it's setting there are adjustments behind the cover
Not suggesting you do it, a sparky should whilst on phone to Sma tech
 
As I mentioned above, SMA do not recommend anything less than 6mm2 conductors for the AC side of a 4000TL for a maximum length of 23.3 meters.

Have a look at the SMA manual here - PDF Download Section 5 - 5.3 - 5.31

Also stated there is:

Cable sizing

The grid impedance of the AC cable must not exceed 1 ohm. Otherwise, the inverter will disconnect at full feed capacity due to excessive voltage at the feed-in point.
The conductor cross-section should be dimensioned such that cable losses do not exceed 1 % at nominal power.

Installing a 4mm2 cable would actually be non compliant with BS7671 (Electrical Regulations) which states:

134.1.1 Good workmanship by competent persons or persons under their supervision and proper materials shall be used in the erection of the electrical installation. Electrical equipment shall be installed in accordance with the instructions provided by the manufacturer of the equipment.

OK, it's not dangerous but the installer has failed to know the installation requirements of the product he's supplied and installed. I'd contact him and point this out.
 
Hi

I had a solar panel system fitted 22 Feb 2012. The system includes a 15 panel sharp 245 array split into 2 strings of 9 and 6 running into a Sunny Boy 4000TL.

They system seems to produce consistently until about midday then cut out for periods if there is a decent amount of sunlight. I have been monitoring the system with Sunny Boy Explorer and noticed if the combined string voltages exceed 500v then the output drops to 0A and 0W. This remains the case until the voltage drops below 500v.
When running normally the volatges for each string are 280-290V and 170-180V. This can then jump to over 300V and 200V and knock the system out. I believe the inverter operates up to 550V. Would changing the inverter to the 4000TL with Reactive Power Control which has a 750V limit cure the problem or is there a more fundamental issue here.
I have also noticed recently that output power has sometimes been exceeding 4.2KWh which seems strange for a system with a stated output of 3.675KWh.
The installers have been around a couple of times and seem a little mystified but have suggested replacing the inverter as a first solution.
If anyone can offer me some advice I would be most grateful.
Cheers
Motters

As others have said the combined Voltage exceeding 500v is not a problem as each of the 2 trackers in your inverter are rated upto 550v each (1100 total). I have looked at the technical data and it states the max input power as 4200w and you state you are exceeding this at certain times. Could this be part of the problem? You would likely generate most power around noon if the panels are on different roofs and different orientations (thats the situation with mine).
 
Hi
Thanks again for all your replies. I have been monitoring the system this morning.Nice bright sunshine, copied these readings
Current [001] 8.014 A
Current (002) 8.556 A
Voltage [001] 263.52 V
Voltage (002) 175.07 V
Power [001] 2112 W
Power(002) 1497 W

Looks nice and healthy, I will be keeping an eye on it to see when the readings jump.
Cheers
Motters
 
Don't think this has been mentioned but have you checked the inverter is set for G83 ? Turn off AC isolator, wait a minute, turn back on and check the lcd display shows G83/1 during the power up procedure.
 
Hi

1143 -No really strong sunshine but this occurred:DC side readings
0.000 A

[TD="class: col1 sum level2"]Current [001][/TD]

[TD="class: colStatus"] [/TD]
0.000 A

[TD="class: col1 sum level2"]Current [002][/TD]

[TD="class: colStatus"] [/TD]
307.55 V

[TD="class: col1 sum level2"]Voltage [001][/TD]

[TD="class: colStatus"] [/TD]
205.41 V

[TD="class: col1 sum level2"]Voltage [002][/TD]

[TD="class: colStatus"] [/TD]
0 W

[TD="class: col1 sum level2"]Power [001][/TD]

[TD="class: colStatus"] [/TD]
0 W

[TD="class: col1 sum level2"]Power [002][/TD]
1146 - Came back on again
Cheers
Motters
 
Don't think this has been mentioned but have you checked the inverter is set for G83 ? Turn off AC isolator, wait a minute, turn back on and check the lcd display shows G83/1 during the power up procedure.

It has been mentioned and possibly a good time for the OP to try this as I'm sure even though the installer has been out twice, no confirmation has been stated yet.....

Do your DC tails go into the inverter separately...... if so I would be removing one set at a time to see what effect that has, but if you are NOT confident to do this, leave it to your installer as high DC voltages could hurt !
 
Don't think this has been mentioned but have you checked the inverter is set for G83 ? Turn off AC isolator, wait a minute, turn back on and check the lcd display shows G83/1 during the power up procedure.

it wouldnt work with g59 setting
 
Hi

1143 -No really strong sunshine but this occurred:DC side readings
0.000 A

[TD="class: col1 sum level2"]Current [001][/TD]

[TD="class: colStatus"][/TD]
0.000 A

[TD="class: col1 sum level2"]Current [002][/TD]

[TD="class: colStatus"][/TD]
307.55 V

[TD="class: col1 sum level2"]Voltage [001][/TD]

[TD="class: colStatus"][/TD]
205.41 V

[TD="class: col1 sum level2"]Voltage [002][/TD]

[TD="class: colStatus"][/TD]
0 W

[TD="class: col1 sum level2"]Power [001][/TD]

[TD="class: colStatus"][/TD]
0 W

[TD="class: col1 sum level2"]Power [002][/TD]
1146 - Came back on again
Cheers
Motters

Assuming the current was running at about 8 (conservative based upon your earlier reading) that would mean the total power would be about 4200w on your 3.6kw system, the same power output it dropped out before. Does it ever drop out at low generation times?
 
Every event logged by the inverter has a numerical code for which there is an explanation in the manual.

From sunny explorer log in as installer and use the export option to export the event log as a CSV file.

You can then post the file or error numbers.
 
Hi
Just exported all the event date and the only codes are:
1 - Incoming
1 - Outgoing
10223 - Time Interval expired
10010 - Restart diagnosis system
No other codes.
The high voltages today did not coincide with high generation situations; cloudy low power generation just the voltage jumped from 260 to 320 and 160 to 220.
thanks again
Motters
 
what are you using to export the event data?

Sunny explorer?

If so, I'd double check you've got the date range sorted out properly to give you eg the last month, otherwise as standard it only gives you the error log from today.

You need to use the calendar bits top right, and highlight the date range you want, then check it's taken properly.
 
Hi
Just checked the country setting on Sunny Explorer and it says "special setting" is this normal or should it say G83 ?
Do I have to use a different login to check the exact country setting ?
I believe the country setting can be seen on the inverter panel during start up. Where exactly on the panel is this information shown.
Thanks again for all the advice.
Cheers
Motters
 
Sunny explorer, Under settings/grid monitoring mine says Country standard G83/1
 
Last edited by a moderator:
If the inverter has not been set for the UK, which sounds like the case here, the installer will have to now get a grid guard code from SMA to alter the settings, as the inverter has now been running.
This is not uncommon, as many installers believe that all inverters are just plug and play and come already set up for the UK.
I hope this helps.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Solar Panel Output cutting out
Prefix
N/A
Forum
Solar PV Forum | Solar Panels Forum
Start date
Last reply date
Replies
43

Advert

Thread statistics

Created
Motters,
Last reply from
Gavin A,
Replies
43
Views
12,375

Advert