This reg states that TNCS or TNS systems do not need the neutral isolated. Is that at sauce or generally?
Why?
What about TT systems?

Thanks

John
 
In a TN system the neutral is considered to be at or relatively close to 0 volts /earth potential as the earthing conductor returns to the source and is connected at the star point where the neutral is also connected making them the same potential.
A TT system has no earthing conductor returning to the source , the earth fault loop impedance is via the general mass of earth through an earth electrode (s) so a difference in potential can exist.
In a 3 phase and neutral TT installation the installation must isolate all live conductors by a 4 pole isolator at the origin
In a TN 3 phase and neutral installation only the line conductors require isolating at the origin
In a domestic installation regardless of earthing arrangement type, a double pole switch must isolate the installation at the origin.
Part 7 electrical installations may also require the neutral is isolated in certain different earthing arrangements
 
Last edited by a moderator:
I could not put it better me self ,when any post goes up I wish they put a page to it on the regs .
 
Thanks Ian. The reference to domestic you make is that 462.1.201 (p121)? Is that because of the assumption that non-domestics are three phase or more to do with functional switching or none of the above? Thanks.
 
The reference to domestic you make is that 462.1.201
that it means of isolation . whether a fuse or isolator .
 
Thanks Ian. The reference to domestic you make is that 462.1.201 (p121)? Is that because of the assumption that non-domestics are three phase or more to do with functional switching or none of the above? Thanks.
Because domestic installations are used by ordinary persons who are prone to careless actions with regards to electricity
 
  • Like
Reactions: buzzlightyear

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Uk

Thread Information

Title
18TH Regs Chapter 46 - 46.2
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
7

Thread Tags

Tags Tags
18th regs

Advert

Thread statistics

Created
John-,
Last reply from
Ian1981,
Replies
7
Views
3,099

Advert