That’s it all complete PASSED.
Basically had 3 faults
my main bond was one of the faults giving a reading of 4.56 should be 0.05 or below

Next fault was the earthing conductor from the starter at the load side was broken basically you do a r1+r2 test to the top of the starter note it then at the bottom and add together for the total r1+r2 so from the load side it was broken so could not calculate zs as a result of this.

Last fault was on the ring circuit basically the conductors were all 2.5 L&N came back at 1.23 the cpc was 3.56 straight away this was noted meaning that our calculated zs would be to high so been recorded as a C2

Then paper work had to be perfect so happy it’s out the way and onto a new course thanks for the help appreciate it.
 
On the practical, we were told not to look for any visual faults as this was covered doing the photo exercise. My faults were high protective bond reading, open circuit on the lights and low IR.
 
That’s it all complete PASSED.
Basically had 3 faults
my main bond was one of the faults giving a reading of 4.56 should be 0.05 or below

Next fault was the earthing conductor from the starter at the load side was broken basically you do a r1+r2 test to the top of the starter note it then at the bottom and add together for the total r1+r2 so from the load side it was broken so could not calculate zs as a result of this.

Last fault was on the ring circuit basically the conductors were all 2.5 L&N came back at 1.23 the cpc was 3.56 straight away this was noted meaning that our calculated zs would be to high so been recorded as a C2

Then paper work had to be perfect so happy it’s out the way and onto a new course thanks for the help appreciate it.
Well done on passing but why should the R2 reading on the continuity of protective conductors be 0.05 ohms or below?
Guidance note 3 makes it clear that this reading is between 2 exposed conductive parts such as pipes and not from the MET to the bonding conductor.
It’s an urban myth badgered around the industry and taught incorrectly by the tutors
 

Reply to 2391-52 practical exam help in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi Guys. Just wondering what people used to practice the written part of the 2391-52 exam? I have the iet exam prep book, which seems more geared...
Replies
4
Views
487
Hi Guys, sorry if posting in the wrong section. I am due to start 2391-52 course soon, and there seems to be from what I have found out, a 3 phase...
Replies
6
Views
491
I have got these questions on 2391-52 inspection and testing but can't remember option of 1st two questions. Please any suggestion will be...
Replies
2
Views
706
Refurbishment of dwelling has taken place and the clients insurance company requires a periodic inspection and test to be carried out, A new...
Replies
18
Views
1K
  • Question
Hi - Just joined the forum as I'm making a career change and am training up. I've come across some mock papers online and am concerned that...
Replies
7
Views
498

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock