lightmates are a brilliant idea.pity they won't work with megger leads.
I believe these ones work with Megger telectrix.
Socket and See ELECACCKIT | ISSWWW.co.uk - https://isswww.co.uk/socket-and-see-elecacckit-electricians-accessory-kit
Discuss 2391-52 practical exam help in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
lightmates are a brilliant idea.pity they won't work with megger leads.
Last fault was on the ring circuit basically the conductors were all 2.5 L&N came back at 1.23 the cpc was 3.56 straight away this was noted meaning that our calculated zs would be to high so been recorded as a C2
Well done on passing but why should the R2 reading on the continuity of protective conductors be 0.05 ohms or below?That’s it all complete PASSED.
Basically had 3 faults
my main bond was one of the faults giving a reading of 4.56 should be 0.05 or below
Next fault was the earthing conductor from the starter at the load side was broken basically you do a r1+r2 test to the top of the starter note it then at the bottom and add together for the total r1+r2 so from the load side it was broken so could not calculate zs as a result of this.
Last fault was on the ring circuit basically the conductors were all 2.5 L&N came back at 1.23 the cpc was 3.56 straight away this was noted meaning that our calculated zs would be to high so been recorded as a C2
Then paper work had to be perfect so happy it’s out the way and onto a new course thanks for the help appreciate it.