robo83

~
May 23, 2016
180
48
103
Birmingham
Hi,

Been to a job with a 2core swa supplying the garage.. The swa has been glanded inside house to CU. But the other end in the Garage has had the swa run in plastic conduit with no gland on the swa so unable to test r1/r2.

However the garage has its own earth rod. So technically the swa is earthed from the house end, with the garage having its own earth rod.

The garage earthing TT is 37.0ohms, would I note this down as the garage r1/r2 circuit. Accepted with the 1667ohms as rcd?
 
Is this an EICR, or are you doing some alterations/additions in the garage. What is the house supply?
 
Is this an EICR, or are you doing some alterations/additions in the garage. What is the house supply?
Do you mean R1+R2? r1 r2and rn are readings for RFCs (Ring Final Circuits)
 
  • Like
Reactions: robo83
Did you mean to quote the OP Pete :(
 
Did you mean to quote the OP Pete :(
Not sure what you are getting at Middy, just trying to say to the OP that r1 and r2 are readings for r1 Live and r2 Earth as a single conductors, I thought he was meaning R1+R2 or am I getting tangled up somewhere?
 
Robo83, can you not get a croc clip on the armouring at all at the garage end? Then you could measure r1 + r2 this way? Midwest and pete, if that was possible, is that allowed?
 
Robo83, can you not get a croc clip on the armouring at all at the garage end? Then you could measure r1 + r2 this way? Midwest and pete, if that was possible, is that allowed?
It's R1+R2
 
  • Agree
Reactions: 1 person
I dont follow...
You are trying to measure the loop of the L and E conductors correct? Which will give you a resistance reading noted as R1+R2 not r1+r2 a small thing but end to end reading r1 r2 and rn are recorded as RFC readings only, and are end to end readings of the L.N and cpc, get the basics wrong and other things will be wrong as well. Of course if you are insulating the armoring from the garage end why would you try and trying to measure the R1+R2 of the distribution cable.
 
Last edited:
Robo83, can you not get a croc clip on the armouring at all at the garage end? Then you could measure r1 + r2 this way? Midwest and pete, if that was possible, is that allowed?

Hum.... Not sure what that would achieve.... Think about what you are testing
 
He is trying to verify earth continuity to the armour of the cable which is not accessible as it is contained within pvc conduit to isolate it from the TT, this earth continuity is applicable to the circuit from the house and nothing to do with the TT.
 
Perhaps we should just wait until the OP clarifies what he/she is doing?

Edit; job wise
 
  • Winner
Reactions: 1 person
yeh but is it a circuit or just a piece of cable? Where is the loop hah!
 
Last edited by a moderator:
  • Agree
Reactions: Pete999
It would be a circuit wouldn't it, I guess it would be protected by an MCB in this scenario? I guess OP needs to clarify that
 
yeh but is it a circuit or just a piece of cable? Where is the loop hah!
Well if it ain't a circuit how does current / fault current flow in it? Being creative, I'm thinking it's a >32A distribution circuit with a 5 or 1 sec disc time from 411.3.2.3 or .4 - at least it would be if I'd done it in 10mm :)
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Birmingham

Thread Information

Title
2core swa, not earth load end.. TT
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
35

Thread Tags

Advert

Thread statistics

Created
robo83,
Last reply from
westward10,
Replies
35
Views
4,016

Advert