Discuss 40 amp MCB live when off? Faulty? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
He has said earlier that there is no circuit connected to this mcb at all… it is a spare way, but he found power on the outgoing side when the breaker was off.Have you verified that there isn't an erroneous connection to another circuit?
Apologies. I read it that there was a cable connected to it, but that it was no longer used.He has said earlier that there is no circuit connected to this mcb at all… it is a spare way, but he found power on the outgoing side when the breaker was off.
OP; It would be sensible to check all the breakers for the same thing now you’ve found one faulty device.