Have you verified that there isn't an erroneous connection to another circuit?
 
Have you verified that there isn't an erroneous connection to another circuit?
He has said earlier that there is no circuit connected to this mcb at all… it is a spare way, but he found power on the outgoing side when the breaker was off.


OP; It would be sensible to check all the breakers for the same thing now you’ve found one faulty device.
 
  • Like
Reactions: pc1966 and DPG
He has said earlier that there is no circuit connected to this mcb at all… it is a spare way, but he found power on the outgoing side when the breaker was off.


OP; It would be sensible to check all the breakers for the same thing now you’ve found one faulty device.
Apologies. I read it that there was a cable connected to it, but that it was no longer used.
 
Thanks, yes, I have tested all breakers. That's how I found this one. I did the full range of tests, including ramp tests etc and recorded all values, before the electrician who will issue the certs comes and does his own. I installed a full RCBO board in my new kitchen (which is the main test job) and this board was previously installed in another space to serve other circuits. It was the only faulty MCB.

For the record, I looked into trading standards in Kent. They hive reports straight off to Citizens Advice. They in turn made it clear that they are not the slightest bit interested in this, and nor would trading standards be either, unless I could identify a criminal individual or organisation.

Hager has no complaints facility on line. Surprising. When I rang customer services, it took some time to explain the problem as the operator in customer services had no idea what an MCB was. It was suggested that I contact the seller. When I suggested in turn that it may be counterfeit or faulty goods, they suggested I return the item to them if I wanted to, at my cost. So that is a no then!

An MTN140 Type B 6kA costs £3.99 with free prime delivery (same or next day) from Amazon. Only £2.46 at Edwardes. It is simply not worth messing around with. In this case I do not believe that the item was counterfeit. It is just faulty, and if they can make them that cheaply (retail must be double ex factory cost) then it is inevitable that some will be defective.

Interesting experience though.
 
  • Like
Reactions: nicebutdim

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Kent
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
40 amp MCB live when off? Faulty?
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
23

Advert

Thread statistics

Created
AJB Temple,
Last reply from
AJB Temple,
Replies
23
Views
2,979

Advert