I have a number of circuits in a not very old Hager sub CU, with split RCDs. All of the active circuits (8 used in a 12 slot dual RCD CU) test fine. RCDs tripping fine under test with Megger MFT. However, I have a MTN B140 (40 amp obvs) MCB in the board that has nothing connected to it. ie unused. It's live (230v) at the busbar terminal as expected, but also live at full voltage at the top terminal even if the MCB switch is off.

All of the other MCB's behave as normal, with the switches operating as expected. It's not tripping the RCD, presumably because it is an unused circuit breaker.

Is this just a faulty MCB? Obviously I can swap it out for another one, and I don't want a faulty component in the board.

I'm more curious than anything. Any thoughts on causation?
 
So it has voltage at the outgoing terminal when off but what do you mean it is not tripping the rcd.
 
Yes, it has 230v live at the outgoing, irrespective of whether the switch on the MCB is in the on or off position. Toggling the switch does not trip the RCB (nor would I expect it to in normal use). There is no circuit connected to this MCB and I have no need or present intention to connect one - it is just a spare.
 
Remove the MCB and fit a Hager blank.
 
Simply a faulty mcb. Can happen.

If there’s no circuit connected, it’s not getting a back feed from somewhere else like you would with interconnected rcd’s… so only explanation is a faulty breaker.

Would be good to know history of installation… was there ever an electric cooker or shower on this breaker? Is there an unused cable cut back in the board of decent size that may have one been connected?
It may even have been faulty from new, came with the board but never used… so never discovered it was faulty.

Yes, take it out, fit a blank.
If you leave faulty breakers in place, then it’s an increased risk of someone in the future using it for something.
 
  • Like
Reactions: pc1966
What test instrument are you using that shows 240v out of the 40amp mcb?
Have you tried removing the mcb and testing continuity?

It could be jammed mechanism or overloaded and contacts welded together.
If when removed it still has continuity then tap the mcb onto a hard surface and retest.
If that doesn't clear the continuity then carefully open it up and see if it's welded together.

But as others above if it's not needed then remove and replace with blank.
And before disposal destroy the MCB so it can't be picked up by someone and used.
 
  • Agree
Reactions: pc1966
Most likely reason is it had been closed on a few too many high current faults, though it might just have been faulty from new (e.g. bit of swarf stuck inside).

Remove and destroy!
 
  • Like
Reactions: DPG
Thanks guys. It is a brand new and previously unused MCB so has never been abused in any way, or had too many trips etc. Anyway I've popped it out and replaced with a spare B132 as I don't have any blanking plates and I want to use the slot for a radial circuit to a utility room in due course.

Cant see anything physically wrong with the MCB but putting a test current through on the bench, it is clearly by-passing the switch as if it is not there. Quite dangerous really as someone could think they are switched off when they are not.

I decided against tapping and such like, as if it is faulty once with swarf or whatever, it can go faulty again as the switch is a sealed unit. Should not happen with a good brand really.

I identified it with a quick live check all round the CU. I use a Megger continuity tester with proving unit, and for testing a Megger MFT 1731. (I know - I am a DIYer but I still understand testing and circuits). Obviously I am not domestic trade so I don't see many faults like this. The MCB unit was actually bought from Amazon (who are a lot cheaper than CEF !) and they are only a few pounds each, but I will return it as faulty anyway.
 
The MCB unit was actually bought from Amazon (who are a lot cheaper than CEF !) and they are only a few pounds each, but I will return it as faulty anyway.
Suddenly I am not surprised! Possibly fake?

I would open it and check, or better still report them to trading standards.
 
Suddenly I am not surprised! Possibly fake?

I would open it and check, or better still report them to trading standards.
Trading standards would be where I was sending it.

also, if you have any others from there, I would replace them with ones sourced from reputable supplier immediately.
 
  • Like
  • Agree
Reactions: DPG and pc1966
Remind me of a Big Clive teardown
 
Okay, try again. Reminds me of a Big Clive teardown
 
  • Informative
Reactions: pc1966
There are times when I hate my phone 🤔
 
Yes, it could be fake I suppose. All of the others came from TLC in Tunbridge Wells - I buy nearly all of my electrical stuff from them. The Amazon one looks absolutely identical in every respect: same plastics, weight, printing etc and same packaging. Hardly seems worth counterfeit fakery for things as cheap as this. I doubt trading standard would take any interest in something under £10 like this.
 
I doubt trading standard would take any interest in something under £10 like this.
It is not the price, it is the risk to safety.

At the very least Hager would want to know if there is a manufacturing fault or there is a dodgy side-trade in fake/failed ones.
 
  • Like
Reactions: DPG
Fair point. I'll think it over how to proceed.
 
Might be interesting to compare the weight with a known genuine one.
 
  • Like
Reactions: DPG
No way could I resist opening that up and having a look.

And definitely report it. If it's a bad batch then action needs taking rather than leaving them in place ready to cause an incident when they don't trip on a fault.
 
  • Agree
Reactions: pc1966
If you do decide to open it up yourself, take plenty of in-focus photos before and during the dismantling process!
 
  • Like
Reactions: Jim_e_Jib and DPG
I weighed it versus a genuine Hager from TLC. Using my bakers scales which weigh digitally to the gram. They are identical. Shaking and it tapping it does not rectify the fault. I can't get it apart non-destructively, so I will be returning it for a refund and have already left a negative review (which may well get blocked).

This is actually the secon Hager MCB we have had fail. We had a defective one in a different CU in a kitchen about 2 years ago, and in that case it just tripped constantly when there was no circuit fault. That one was identified by an electrician who didn't bother with any tests (and said he was not certified anyway - he was near retirement) he just swapped the wiring over and put tape over the dud. I keep meaning to whip it out actually.
 
Have you verified that there isn't an erroneous connection to another circuit?
 
Have you verified that there isn't an erroneous connection to another circuit?
He has said earlier that there is no circuit connected to this mcb at all… it is a spare way, but he found power on the outgoing side when the breaker was off.


OP; It would be sensible to check all the breakers for the same thing now you’ve found one faulty device.
 
  • Like
Reactions: pc1966 and DPG
He has said earlier that there is no circuit connected to this mcb at all… it is a spare way, but he found power on the outgoing side when the breaker was off.


OP; It would be sensible to check all the breakers for the same thing now you’ve found one faulty device.
Apologies. I read it that there was a cable connected to it, but that it was no longer used.
 
Thanks, yes, I have tested all breakers. That's how I found this one. I did the full range of tests, including ramp tests etc and recorded all values, before the electrician who will issue the certs comes and does his own. I installed a full RCBO board in my new kitchen (which is the main test job) and this board was previously installed in another space to serve other circuits. It was the only faulty MCB.

For the record, I looked into trading standards in Kent. They hive reports straight off to Citizens Advice. They in turn made it clear that they are not the slightest bit interested in this, and nor would trading standards be either, unless I could identify a criminal individual or organisation.

Hager has no complaints facility on line. Surprising. When I rang customer services, it took some time to explain the problem as the operator in customer services had no idea what an MCB was. It was suggested that I contact the seller. When I suggested in turn that it may be counterfeit or faulty goods, they suggested I return the item to them if I wanted to, at my cost. So that is a no then!

An MTN140 Type B 6kA costs £3.99 with free prime delivery (same or next day) from Amazon. Only £2.46 at Edwardes. It is simply not worth messing around with. In this case I do not believe that the item was counterfeit. It is just faulty, and if they can make them that cheaply (retail must be double ex factory cost) then it is inevitable that some will be defective.

Interesting experience though.
 
  • Like
Reactions: nicebutdim

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Kent
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
40 amp MCB live when off? Faulty?
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
23

Advert

Thread statistics

Created
AJB Temple,
Last reply from
AJB Temple,
Replies
23
Views
2,969

Advert