underpar12

Called to agents shop today no sign lights , on further investigation I think it could be the relay, the relay supplies a couple of timed circuits. two circuits work fine and the sign light do not .not sure how the relays work never fitted one before .
 
Terminals 2 & 7 are the coil terminals, which is where the input from the timeclock or photocell etc connect. The rest are common, NO & NC terminals depending on what you are trying to achieve.

If the relay is switching lights then the NO terminals will be used.
 
If it's a neon sign and the relay/contactor is testing fine then check that kids haven't played with the firemans switch.



images.jpeg
 
Thanks for reply ,the relay looks very busy inside the enclosure with cables in connector blocks .what confused me is the relay is switching two circuits ok. The relay is very hot to touch.think I will be changing tomorrow.
 
If the relay has 3 ccts connected to it and 2 of them are working then it's a fair bet that it's not the relay that's the problem. Just test it first, it will probably saveyou time and money that way. They can feel pretty warm to touch, if it doesn't smell like burning or overheating then don't worry about it being warm.
 

Reply to Advise regarding relays in the Australia area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top