I would appreciate some advice on the following as i am not a full time spark and most of my electrical work is normally limited to minor works.

I was at a clients house in the week and while talking she mentioned that she needed to get a 3 phase supply installed at a cost of £6.5K + for her under floor heating which apparently draws 80A. The spark who done the re-wire in January thinks the total load is going to be around 135A which includes everything in the house.

He has said all the db's need changing to 3 phase.

There house is large but there are no electric showers, cooker is gas so the only items are really pull any current are on the ring and kitchen appliances.

I had a look quick look at the current system which has a 60A fuse on the incoming and then 2 x 12 way boards, 1 of which is for the underfloor 4 x 20a mcbs - Hall, living room, kitchen and small bathroom.

I think the figure of 135A is way out and no diversity has been allowed and there would be no need to change the db's either.

Would i be correct in thinking that no diversity is allowed for the underfloor heating but more common sense in that she has said that there would only ever be a maximum off 2 x areas on and never all 4.

I am due back on Friday to finish some AV and security stuff so i was thinking of advising possibly getting the 60A upgraded to 80A or 100A and also clamp testing the supply with the 2 x areas of the underfloor on and some other items to get some sort of idea on the actual load.

Thanks
 
So is this an existing installation with all of the loads currently connected and working?

If it is then I'd suggest that a 60A supply is enough based in it currently working fine on an 60A supply.

What is the actual load of the underfloor heating? Just because it has a 20A mcb does not mean it will use 20A when operating!
If no data is available just measure the resistance of the underfloor mats/cables and calculate the power.
 
Sorry forgot to put that the underfloor MCBS have been taped off and the underfloor has never been used due to the above.

No data available for the underfloor load as the job has been a bit of nightmare for the client.
 
Forget the 3 phase nonsense, a house with no electric cooking or showers won't ever achieve a constant current of 20A, and then 4x underfloor mats will achieve a degree of diversity whatever the damn OSG says!
 
Sorry forgot to put that the underfloor MCBS have been taped off and the underfloor has never been used due to the above.

No data available for the underfloor load as the job has been a bit of nightmare for the client.

Just measure the resistance of the underfloor heating and calculate the power!

I'd be happy to bet that a house without electric cooking or showers will never achieve a steady current of 20A.
 
think the spark that did the rewire needs to go back to the fast track training centre. do week 6. 135A my arse!
 
Sorry forgot to put that the underfloor MCBS have been taped off and the underfloor has never been used due to the above.

No data available for the underfloor load as the job has been a bit of nightmare for the client.

If the U-Floor heating is already installed, try powering up 1 zone at a time and see what the load is.

I'll bet there's a fault on one zone and the last Spark thought it was overloading in normal use and switched it all off.
 
I would, clamp it,whack all on see the kind of load you are pulling.

I'd be wary of doing that, if it is a hefty load of underfloor then turning it all on at once might be enough to tip an old 60A fuse over the edge.
I'd switch the underfloor heating on gradually (a good few hours between each) to give diversity a chance to come in to play.

Also there is no point in just measuring the max connected load, as it does not represent the maximum realistic demand. You may still end up thinking you need a bigger supply when you don't.

Clamp meters only give a snapshot of the current demand at a particular point in time, you need to record current over a period of time, a week for example, to really know what is going on.
 
If as you state the house is large then an upgrade to an 80A service fuse should be more than sufficient for the present installation and future additions.

As Dave suggested i'd bring these four UFH mats on gradually, i bet as others here say, that you'll not see 135A or anywhere near it....


BTW what's the total square meterage of UFH mats. Oh and i'm sure the installing electrician left the homeowner with all the details of the systems to register the them for warranty purposes etc!! loll!!
 
sorry that guy is a muppet?

having 3 single phase boards each fed by a different phase would be fine

i could say the total load in my house is over 100amps

both showers pull 40 amps and the hob 50 acording to the manufacturer

but i doubt it would get anywhere near that
 
Slightly off point but £6.5k for a three phase supply! Did the client not ask this question before they put in the uf heating to begin with. If there are not cooking with electric I take it there is gas on site so for £6.5k they could have put a wet uf system is with far lower running costs. Sounds odd to me.
 
Hopefully there are bills/receipts for the underfloor heating somewhere? Or a contact number for the installers?

With a quick bit of research I am sure you will find the loading.
ie. An average sized room of say 20m² X a few examples found via google at 200w/m²
 
Hopefully there are bills/receipts for the underfloor heating somewhere? Or a contact number for the installers?

With a quick bit of research I am sure you will find the loading.
ie. An average sized room of say 20m² X a few examples found via google at 200w/m²
Oh dear me!
Perhaps I've been doing things wrong all these years, I rely on this machine thingy that measures resistances.
 
Oh dear me!
Perhaps I've been doing things wrong all these years, I rely on this machine thingy that measures resistances.

Shouldn't need to test these UHM's the homeowner should be in receipt of all the product documentation that will state total areas installed and W/m2 values!!!

But thinking about it, it's more likely that the homeowner has been given nothing apart from the bill for the installation!! .... lol!!
 
It has already been stated that the installer hasn't given over any paperwork.
So it's a case of simply testing the mats and calculating the power, granted it may not be spot on to the nearest watt, but a lot better than the other suggestion of guessing the watts per square metre!
 

Reply to Domestic 3 phase advice in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock