I would, clamp it,whack all on see the kind of load you are pulling.

I'd be wary of doing that, if it is a hefty load of underfloor then turning it all on at once might be enough to tip an old 60A fuse over the edge.
I'd switch the underfloor heating on gradually (a good few hours between each) to give diversity a chance to come in to play.

Also there is no point in just measuring the max connected load, as it does not represent the maximum realistic demand. You may still end up thinking you need a bigger supply when you don't.

Clamp meters only give a snapshot of the current demand at a particular point in time, you need to record current over a period of time, a week for example, to really know what is going on.
 
If as you state the house is large then an upgrade to an 80A service fuse should be more than sufficient for the present installation and future additions.

As Dave suggested i'd bring these four UFH mats on gradually, i bet as others here say, that you'll not see 135A or anywhere near it....


BTW what's the total square meterage of UFH mats. Oh and i'm sure the installing electrician left the homeowner with all the details of the systems to register the them for warranty purposes etc!! loll!!
 
sorry that guy is a muppet?

having 3 single phase boards each fed by a different phase would be fine

i could say the total load in my house is over 100amps

both showers pull 40 amps and the hob 50 acording to the manufacturer

but i doubt it would get anywhere near that
 
Slightly off point but £6.5k for a three phase supply! Did the client not ask this question before they put in the uf heating to begin with. If there are not cooking with electric I take it there is gas on site so for £6.5k they could have put a wet uf system is with far lower running costs. Sounds odd to me.
 
Hopefully there are bills/receipts for the underfloor heating somewhere? Or a contact number for the installers?

With a quick bit of research I am sure you will find the loading.
ie. An average sized room of say 20m² X a few examples found via google at 200w/m²
 

Reply to Domestic 3 phase advice in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone, I have been asked to pull in some new 3 phase supplies for 7 new welders which do not require a neutral connection. The client has...
Replies
4
Views
768
hi guys / girls , any advice would be appreciated, So the situation is a domestic property has a 3 phase supply , from the service head we have 3...
Replies
1
Views
311
Good morning, So I’m working on an existing 3 phase solar system and the customer wants a way to use the huge mass of exported solar on their...
Replies
3
Views
990
Hi there, I built a house with ground source heating 5 years ago and it's a fairly large house so I have 3 phase supply 80 amps per phase. I had...
Replies
7
Views
1K
I'm after advice on how best and safely to do a friends Fuseboard upgrade. Current setup is a Wylex 6 Way board with MCBs of 2x 6A, 2x 32A and 30A...
Replies
2
Views
266

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock