Discuss Earth rod query in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

All this talk about earth rods and I have one query.

When measuring an earth rod resistance and trying to get it down to 10 ohms are we talking about the rod resistance itself or are we talking about the EFLI?

If we are talking about the rod resistance being ten ohms then what about the impedance of the transformer rod which could be twenty ohms itself so no matter how low we get our earth rod resistance we are never going to get lower than the impedance of the transformer rod.

Admittedly there will be parallel paths involved through other peoples bonding etc but when talking about a low Ra are we talking just about the earth rod or are we talking about the total earth fault loop?

Thanks.

In theory, when we use an earth fault loop impedance tester, the instrument measures Ze because it gives us Ra for the earth electrode and earthing conductor, the resistance of the supply transformer electrode, the transformer winding impedance and the resistance of the supply line conductor from the transformer.
 
If you take this argument to the extreme, once you start ignoring one regulation why not just ignore them all? Then you don't need to bother with an earth at all!
 
what about the impedance of the transformer rod which could be twenty ohms itself


You would have to search long and hard to find a sub-station earthing system anywhere near that 20 ohm max. Here they do use multiple rod positions and the 2.4/3.2m rods, for both the MV and the LV side of things!!

The best way to test an earth electrode of any type, is with a dedicated 3/4 pole earth test kit. unfortunately most of the even half decent ones are too expensive for the self employed electrician that only comes across TT system from time to time.

Some MFT's have a facility for earth testing, but then your only getting what you pay for, so the facilities are very basic...

 
Why is there an 8m min distance on your diagram?




You don't have to answer that question of course :)
Way out of my instrument league.
 
Last edited by a moderator:
The reason for the 8 metres is so the LV Earth does not pick up voltage from an HV Earth fault and transfer it to the LV system.

There is a rule that if an HV Earth is 1 Ohm or lower the LV and HV Earths can be combined but don't ask me why.

An HV Earth is also known as an Earth nest (multiple Rods perhaps) but again don't ask me why but I like the expression an "Earth nest".
 
Last edited:
Last edited by a moderator:
As La Poste has said to prevent imported MV faults appearing on the consumers system.
The drawing does show a removeable MV / LV link. All the transformers I’ve installed have had the MV to LV solidly linked.

That's because they were all probably well under the 1 ohm mark.... lol!!!
 

Reply to Earth rod query in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, I did my first EICR on a TT system today and the Zs was a lot higher than Ze+R1+R2 on everything. Zs was around 3.5 ohms on all of the ring...
Replies
10
Views
970
OLDBOY
O
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
951
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Afternoon all I am looking for some advice as on what to with the suppliers earth after a conversion to a TT system. Current issue is earthing...
Replies
10
Views
2K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
492

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock