Discuss EV Charger in the UK Electrical Forum area at ElectriciansForums.net

Cheers mate. Not that it's breaking the bank, just that it's in a hell of an awkward location. Gas and electric income within a couple of foot as well as 3 drains ?? I think I will just bang another rod in to be on the safe side but just hoping I don't hit anything!
Next time you look at an EV job if rodding is going to be a nightmare order a PEN fault relay and you wont have to use an earth rod .
 
I have just installed my first EV Charger yesterday. I have installed using a 6mm twin from the non RCD side of the consumer unit on a 32a type b MCB. The length of run is around 5 metres and is contained in 20mm round conduit.

The charger I have fitted is a Rolec with a built in type A 30mA RCBO. I have installed an earth rod below the charger as I was told EV chargers can rely on the earth of a TNC-S system.

Upon testing j had a reading of 347 ohms on my Rod and 24.8ms on my RCD. my question is, would this be sufficient as it is protected by a 30mA RCBO therefore the maximum reading permittable is 1667ohms or am I wrong and does it have to be below 200ohms?? 50volts (touch voltage / 0.03 = 1666.66.

Thanks guys! Go easy, this is my first post!
Tidy install with the conduit etc Not a fan of Rolec units myself as the quality is not there, if getting into the EV game start with some other brands. for £60 more you can get a zappi and the hub if going down olev route from the main suppliers and dont need an earth rod or upfront RCD. so much better in terms of quality and features.

Personally I wouldn.t be happy with a reading that high on an earth rod, If ground conditions permit I would look to get it in a lot deeper (use an sds attachment to drive it in ) or add additional rods. if not possible then the Matt: devices or the Garo alternative would be my go to device.

As mentioned some Renault EVs throw a tantrum on anything over 100 ohms. so bear this in mind.

The EV game is getting quite strict now on risk assessments and pre works surveys, NAPIT will soon be looking to inspect an ev charger install on annual assessments for those involved in the sector, have heard rumours NICEIC will be following suit, if you install chargers then they will ask to see one on the annual assessment either instead of or in addition to other work. as a lot of people are installing them with no regards for the condition of the existing install or risk assessments. OLEV are now asking for additional documents and wont be long before they ask for the pre install site survey to be documented and submitted along with DNO forms etc. I am all for it as I have seen some truly horrific installs, In one case
 
I have just installed my first EV Charger yesterday. I have installed using a 6mm twin from the non RCD side of the consumer unit on a 32a type b MCB. The length of run is around 5 metres and is contained in 20mm round conduit.

The charger I have fitted is a Rolec with a built in type A 30mA RCBO. I have installed an earth rod below the charger as I was told EV chargers can rely on the earth of a TNC-S system.

Upon testing j had a reading of 347 ohms on my Rod and 24.8ms on my RCD. my question is, would this be sufficient as it is protected by a 30mA RCBO therefore the maximum reading permittable is 1667ohms or am I wrong and does it have to be below 200ohms?? 50volts (touch voltage / 0.03 = 1666.66.

Thanks guys! Go easy, this is my first post!
Hi Tomos. Can I ask if this is PME? You have said you have installed an earth rod because EV charges can rely on the earth of a TNCS which i dont quite understand. Did you mean 'couldn't rely' on earth of the TNCS?

Also, where have you actually terminated the earth cable you have installed. In the charging unit? If so, wouldn't that be classed as utilising note (ii) of regulation 722.411.4.1 which means you would have to get the Ra much much lower (in reality you would not be able to get it low enough without multiple earth rods as it needs to be around 1ohm).
 
Tidy install with the conduit etc Not a fan of Rolec units myself as the quality is not there, if getting into the EV game start with some other brands. for £60 more you can get a zappi and the hub if going down olev route from the main suppliers and dont need an earth rod or upfront RCD. so much better in terms of quality and features.

Personally I wouldn.t be happy with a reading that high on an earth rod, If ground conditions permit I would look to get it in a lot deeper (use an sds attachment to drive it in ) or add additional rods. if not possible then the Matt: devices or the Garo alternative would be my go to device.

As mentioned some Renault EVs throw a tantrum on anything over 100 ohms. so bear this in mind.

The EV game is getting quite strict now on risk assessments and pre works surveys, NAPIT will soon be looking to inspect an ev charger install on annual assessments for those involved in the sector, have heard rumours NICEIC will be following suit, if you install chargers then they will ask to see one on the annual assessment either instead of or in addition to other work. as a lot of people are installing them with no regards for the condition of the existing install or risk assessments. OLEV are now asking for additional documents and wont be long before they ask for the pre install site survey to be documented and submitted along with DNO forms etc. I am all for it as I have seen some truly horrific installs, In one case
Thanks mate! I think I will be putting another rod in, with a threaded end so I can attach another rod to drive it down deeper. I will get the reading down to below 200ohms! The car being charged is a BMW i3 ?

I have been made aware of rolec chargers not being the best on the market, but this one was supplied by the customer.

Thank you for your feedback mate. I will let you know how I get on ?
 
Hi Tomos. Can I ask if this is PME? You have said you have installed an earth rod because EV charges can rely on the earth of a TNCS which i dont quite understand. Did you mean 'couldn't rely' on earth of the TNCS?

Also, where have you actually terminated the earth cable you have installed. In the charging unit? If so, wouldn't that be classed as utilising note (ii) of regulation 722.411.4.1 which means you would have to get the Ra much much lower (in reality you would not be able to get it low enough without multiple earth rods as it needs to be around 1ohm).
Hi mate. Yes I was meant to put cant rely on the earth of a TNCS system. I have terminated the earth cable from the earth rod to the earthing terminal within the car charger. The earth coming from the installation i have put in a Wago but connected the earth at the house end so the supply cable is protected.
 

Reply to EV Charger in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I’m wondering if anyone would be able to tell me if I have a looped supply in my property as I’m looking to install an EV charger.
Replies
4
Views
318
I note that in answer to another EV Charger question a member suggested a 40A breaker would be preferred to a 32A because of many hours at...
Replies
34
Views
2K
I would like to hide the cable to an EV charger. The consumer unit, meter cabinet and charger would all be on the same wall. About 5 metres from...
Replies
19
Views
2K
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
859

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock