I'll start with the problem.

I've installed two Hive Mini Pro 3 EV chargers, and both have had the same fault, which I think I've now isolated to the CT Cable (Not the clamp or its direction).

Essentially if I connect the CT Cable to the EV Charger and enable smart charging, the EV Charger will randomly report an earth fault. If I disconnect the CT Cable and disable smart charging, the EV Charger works perfectly fine.

I have extended the CT Cable provided with the clamp, in the same way at both installations using a Doncaster EV Ultra Cable which contains a shielded CAT 5e cable. Then connected one twisted pair to the CT Clamp Cable using Wago's, the other end of the twisted pair to the EV Charger.

The install instructions for the Hive does suggest that if a shielded data cable is used the sheath needs to be earthed, but I can't work out how.

Has anyone else have experience of the Hive Mini Pro 3 chargers, and if so have you come across a similar problem. How did you extend the CT Clamp cable if you needed to ?
 
I'll start with the problem.

I've installed two Hive Mini Pro 3 EV chargers, and both have had the same fault, which I think I've now isolated to the CT Cable (Not the clamp or its direction).

Essentially if I connect the CT Cable to the EV Charger and enable smart charging, the EV Charger will randomly report an earth fault. If I disconnect the CT Cable and disable smart charging, the EV Charger works perfectly fine.

I have extended the CT Cable provided with the clamp, in the same way at both installations using a Doncaster EV Ultra Cable which contains a shielded CAT 5e cable. Then connected one twisted pair to the CT Clamp Cable using Wago's, the other end of the twisted pair to the EV Charger.

The install instructions for the Hive does suggest that if a shielded data cable is used the sheath needs to be earthed, but I can't work out how.

Has anyone else have experience of the Hive Mini Pro 3 chargers, and if so have you come across a similar problem. How did you extend the CT Clamp cable if you needed to ?
Was this issue solved?
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
UK
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Correct Method to extend CT Clamp cable for EV Charger (Also should it be earthed)
Prefix
N/A
Forum
Domestic Electrician Forum
Start date
Last reply date
Replies
1
Unsolved
--

Advert

Thread statistics

Created
vwes59,
Last reply from
Rhystang,
Replies
1
Views
671

Advert