wobblymike

i am about to build a partition wall in my daughters house to split one big bedroom into 2 for my grandchildren. Iam going to install 2 double sockets on each side of the new wall. There is one double socket in the bedroom at present and my intent is to split the ring under this socket by cutting one of the cables and inserting the new cable run via 2 30a junction boxes. When i polled up the floorboard yesterday I was surprised to see only 1 set of connections to the socket via a single cable. I confirmed this by opening the face plate and confirming there was only 1 set of connections. This indicates that the socket is a spur which is very surprising as it is the only socket in the room. Obviously I cannot run the new cable run from a spur. Am i missing something here?,
 
you could fit a FCU before the existing socket then spur off your new sockets from there. make all connections in back of accessories, then they are accessible.
 
i am about to build a partition wall in my daughters house to split one big bedroom into 2 for my grandchildren. Iam going to install 2 double sockets on each side of the new wall. There is one double socket in the bedroom at present and my intent is to split the ring under this socket by cutting one of the cables and inserting the new cable run via 2 30a junction boxes. When i polled up the floorboard yesterday I was surprised to see only 1 set of connections to the socket via a single cable. I confirmed this by opening the face plate and confirming there was only 1 set of connections. This indicates that the socket is a spur which is very surprising as it is the only socket in the room. Obviously I cannot run the new cable run from a spur. Am i missing something here?,

Experience and qualifications?
 
  • Like
Reactions: 4 people
Testing, Certification & Notification to LABC ???your breaking the law if you don't do the latter
 
telectrix thankyou for that thought can you offer any thoghts as to why the only socket in the room appears to be a spur
 
Mate, this is really simple stuff that any decent spark will be able to sort for you easily. Please get someone in to do this for you, especially as you say it's for your grandchildren!!!!! Without seeing the layout, no-one on a forum can direct you as what to do. For example, if I was doing this job, I'd do testing at the distribution board to confirm that the ring was actually a ring, before doing anything else.
 
telectrix thankyou for that thought can you offer any thoghts as to why the only socket in the room appears to be a spur

Could be any reason from the circuit being a radial, or more likely it's just spurred off the ring. This is why you need to verify what the circuit is to give you/us a better idea of what can be done
 
There is nothing wrong with the occasional spur and they are commonly found. However, and you need to absorb this - no matter how competent you are (and I get an impression that you are, please don't get me wrong) at DIY and 'know how things work' the installation of extra wiring/sockets etc is now governed by Part P of the building regs and you are legally required to notify to your local area building control what you are doing and that the end result meets current regs, is tested and certified etc.

On a practical note, if it IS a spur then you need to identify where it's fed from. If it's a double socket on a ring elsewhere then the easiest thing to do is to make that spurred socket into a 13a fused spur (doesn't even need to be a switched one, you just need the fuse) and then feed the other two new sockets from it. However, if it's actually a radial (point to point) circuit and you happen to have found the last point then so long as the rest of the circuit is OK and meets the applicable regulations then you can just extend it.

BUT - how are you to know about the applicable regs and be able to test that circuit to BS7671:2008 and know that it will not be in danger of harming said grandchild afterwards?
 
  • Like
Reactions: 1 person
as above posts, but have to disagree with the LABC involvement. this is not a notifiable job, but should be carried out in accordance with current regulations, tested and a minor works certificate completed. for what it will cost to get a qualified sparks in, that's the best option.
 
  • Like
Reactions: 1 person
I find it incredible.......I bet he wouldn't mess around with the gas but he's happy to faff with the electrics. :(
 
Tel, Spin - yes, fair comment! Get so used to the same routine it's easy to forget. But, an interesting technical point, when does 'extending a circuit' (non notifiable) start to cross over with fundamentally changing the characteristics of a circuit so far as Zs and different CPD's is concerned?

AND - no one has yet to mention the letters R, C & D.
 
Pretty grey area on the online notification, I was told to but extra sockets (not in special location) as "Other".....when you notify "Other" in comes as Notifiable to LA, I'm going to question it this week.
 
wobbly, if you post your location, i'm sure one of us is close to you.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
exyending ring main
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
64

Advert

Thread statistics

Created
wobblymike,
Last reply from
Paul.M,
Replies
64
Views
5,483

Advert