Sep 20, 2022
3
1
33
Manchester, UK
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)
Business Name
RicoRepairs
Hi all, so just moved into a new property, the light fitting/rose was removed from the living room, nothing looks to be shorting (But there is a single neutral with no connector block?) but the breaker trips straight away. There are 4 fittings on this floor, none with bulbs in, none with any sign of issues with the fittings.

So is there an easy way to diagnose where the short is? (If that's what it is)

Thanks for any help here ;)

Untitled-2.jpg

Untitled-1.jpg
 
The most common thing to have happened here is a dead short has been created across live and neutral. One of the blacks is likely to be a live return from the switch and not a neutral. Why one is not connected is not clear but it may have broken off, an electrician should be able to fathom it out and test to ensure all is okay. If they are all connected by way of those unenclosed block connectors then that also needs addressing.
 
  • Like
Reactions: DPG and James
Ok :/ I was kind of thinking as only one light has been removed, and it was more than likely all fine before that, that i wouldn't have to get a spark round ... i would like the chance to be able to fathom it out myself (With a small amount of help/advice from the internet) ;)
 
As mentioned, there is a dead short between live and neutral.
I’m not sure why one red is on its own though??? They maybe just couldn’t fit all 3 together.

Search Loop-in ceiling rose, or 3-plate wiring to see diagrams… but what you need is a red and black coming from source… a red and black going to next light….. and a red and black going down to the switch.

3 reds together are all live… 2 blacks are neutral, remaining black is the switched live.


You could put each of the reds and blacks in separate connectors until you can organise an electrician.

Then the lights up to this point would work…. But the rest of the circuit would be functionally disconnected.
 
  • Like
Reactions: DPG
My guess is that the previous owner removed a light fitting without carefully marking what was what, then decided to make it "safe" by fitting a connector block on the bare wires. Unfortunately, they got it wrong, and the cable to the switch has ended up connected directly to the incoming supply cable, with the result that there's a dead short if the room light switch is on.
 
Ok, thanks for the replies and advice, I will dig deeper when I have time.
 
  • Like
Reactions: DPG

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Manchester, UK
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)
Business Name
RicoRepairs

Thread Information

Title
Ground floor lighting trips circuit breaker.
Prefix
N/A
Forum
DIY Electrical Advice
Start date
Last reply date
Replies
5

Advert

Thread statistics

Created
RicoRepairs,
Last reply from
RicoRepairs,
Replies
5
Views
2,323

Advert