OP
- Reaction score
- 0
so terminal 3 in hive reciever would go to 5 in wiring centre, and 4 in hive would go to 7 in wiring centre as i said?? is that correct.I'd remove the connector strips from that terminal box and connect it up as a standard S plan system using wago connectors.
I'd probably feed the boiler directly from the sfcu and take a 4 core flex (L, N, S/L and E) from the boiler to the terminal box using terminal 2 to feed the external controls.
so from terminal 2 (switch live out) in boiler where would you take it to on wiring centre.
does that mean terminal 1 (switch live in) in boiler you would not need to connect a wire..
i thought the brown in the zone valves where perm lives but looks as if its the grey wires thats perm lives.
its just a head scratcher for me this one its been 15 year since i done this setup but without using a hive.