Thanks for your help, I understand it all apart from the factor (1.2). What factor am i applying?It's a poorly worded question. You are right that you would ideally have more information.
My understanding to hopefully set you in the right direction is:
1) They want you to understand that Zs = Ze + (R1+R2)
That is: the loop impedance measured at the end of a final circuit consists of the live coming from the supply transformer into the consumer unit, the live from the CU to the end of the circuit (R1), the CPC back to the main earth terminal (R2) and the path through real earth back to the supply transformer (which will vary according to the earthing system in use).
2) They have given you the measured value at the end (Zs) and the supply portion (Ze).
So exactly as you said, taking one from the other gives you the theoretical impedance of the final circuit only.
(there are reasons you wouldn't ideally do it like this in many real life situations, I'm ignoring them for now!)
3) They want you to understand that resistance changes with temperature; the test was at 20 degrees, and the cable will be at 70 degrees.
This can sometimes matter, if you apply ohms law you will see that if the resistance changes, the current will change, and ultimately the fault current needs to be enough to operate a fuse or circuit breaker.
4) There is a factor which they give you (1.2) which comes from a calculation contained in the On Site Guide to adjust a resistance for a temperature of 70 degrees when the ambient temperature is between 10 and 20 degrees.
So I believe it comes down to find the impedance of the final circuit (which you did already) , and apply the factor.
I hope that helps - keep asking questions if not.
(I'd also reassure you that there is usually a much easier way to handle this in many real life situations!)