Anybody know where I can find Max Zs values for BS88-2 fuses over 200A please? The regs only go up 200A. I know I can contact manufacturers and ask them, but wondered if there is a quick reference anywhere? Thanks
 
Think you can apply the method used in graphs.... Try manufactures data .
if its 0.5 for 100A then must be 0.25 for 200A and so on ????

- - - Updated - - -

Just an example
 
Max Zs = Uo / Ia

Ia is the current an amps causing the disconnection of the device within the time specified.
 
  • Like
Reactions: 2 people
Get yourself the max zs app it's great shows me that 200A fuses allow 0.15 factored or 0.20 unfactored
 
But most just go upto 200 I thought anyway
 
Just paid £1.99 for i-phone :icon9:..... handy app though :icon7:

Pehhh!!! iphone.......I spit on the iphone......but thats coz I cant/wont pay the money for one..lol Or should I say, are lass wont let me pay for one..lol. But I cant help feeling that its taking away the enjoyment of looking it up my self.lol

Soon there will be an app for designing installs etc..just takes all the fun out of it!lol

Still, good app though
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Max Zs Values
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
13

Thread Tags

Tags Tags
max values

Advert

Thread statistics

Created
sparx northeast,
Last reply from
Jay Sparks,
Replies
13
Views
3,136

Advert