It will also abort the test if the touch voltage on the Earthing rises above the pre-set parameter, this is usually set for 50V, but some testers (mine can) can also be set for 25V, so check this setting is correct at 50V.
Iam not familiar with your MFT, so cannot help with the setting up.
Just to add, even if your meter is set correctly but the earthing is inadequate, this may rise above 50V and abort the test, also make sure your test leads have a good connection.