Non Registered Spark wiring NewBuild

Discuss Non Registered Spark wiring NewBuild in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
44
Hi all
Went to a Newly Built Granny-Flat last week on behalf of MK's Switch Exchange Program
Opened the CU to find
  • spaghetti Junction,
  • No Labels,
  • Tails half out of Main Switch,
  • 16mm SWA on a run of 50m
  • SWA Armor not earthed
  • PME brought over from main house
  • 50A MCB and RCD protecting SWA
  • 3 x 8.5kW Showers in Granny Flat - (Don't know why 3)
  • No Bonding anywhere

Certificates:
  • No Property Name
  • Customer was the building company
  • Ze results mixed with Zs results
  • Non-Body Certs
  • No Signature on bottom of Certs

Gave the Electrician a call - details found in designer section only - asked for his registration number - reply "C&G 2382 and C&G 2391 I think!"

Asked for NAPIT, NICEIC, etc - reply what are they!

He recalls wiring the house - he didn't know he had to be registered


Called LABC - their reply:
  • No Building Control Certification
  • No Building Control Notice for Electrics
  • No Building Control Notice for Gas
  • No Building Control Notice for Insulation
  • No Building Control Notice for Windows
  • No Building Control Notice for ANYTHING!
  • Only thing they could find was Planning Permission which the customer applied for

Customer spent £85,000 for this build

Electrician is from Manchester Area - Worked down in Pembrokeshire, Wales on this one job
I don't know if I can post the name of the construction company or Electrician - MODs advise please
 
the building is subject to planning control anyway, so the electrician does not need to be with niceic, elecsa etc. as long as LABC are satisfied he's competent, all that's needed is for LABC to receive a copy of the EIC. as for the problems with the installation itself, that's another issue.
 
  • No Labels
  • Tails half out of Main Switch
  • 16mm SWA on a run of 50m
  • SWA Armor not earthed
  • PME brought over from main house
  • 50A MCB and RCD protecting SWA
  • 3 x 8.5kW Showers in Granny Flat
  • No Bonding anywhere

How are any of these complaint? - im sure I dont need to quote regs they dont comply with


Same goes for the EIC - Not worth the paper its written on!
 
  • No Labels
  • Tails half out of Main Switch
  • 16mm SWA on a run of 50m
  • SWA Armor not earthed
  • PME brought over from main house
  • 50A MCB and RCD protecting SWA
  • 3 x 8.5kW Showers in Granny Flat
  • No Bonding anywhere

How are any of these complaint? - im sure I dont need to quote regs they dont comply with


Same goes for the EIC - Not worth the paper its written on!

No labels- hardly going too do any harm to anyone is it
TAils not terminated properly- so the rest of the live parts in the DB are all fully enclosed?
16mm SWA- What problem here?
SWA Not earthed- Is the SWA used as a CPC? or is it run where it needs to earthed?
PME- DNO responsibility? Although no problem with extending it
50 MCB- sounds like it is doing its job properly
3 showers- No problem here
No bonding- are there any extraneous conductive parts?

So aside from the top 2 pretty compliant so far unless you answer the questions I have asked
 
this is a thread that needs a pic of the CU with the lid off, so we can see if it's a bodge or not.
 
No labels- hardly going too do any harm to anyone is it
No RCD, Circuit Identification - not sure if a reg but good practice as these are included in the CU
TAils not terminated properly- so the rest of the live parts in the DB are all fully enclosed?
Tails not in properly - and not cut tidy - only 3 cores connected!
16mm SWA- What problem here?
50m Run - Preferably 25mm would have been better to avoid voltage drop!
SWA Not earthed- Is the SWA used as a CPC? or is it run where it needs to earthed?
SWA Buried underground
PME- DNO responsibility? Although no problem with extending it
Regs State this must be TT
50 MCB- sounds like it is doing its job properly
RCD Discrimination
3 showers- No problem here
if 2 Showers Running - MCB Tripps - 4 Bedrooms for all family members - usual situation for this customer
No bonding- are there any extraneous conductive parts?
All Pipework is metal

Check your regs!

- - - Updated - - -

this is a thread that needs a pic of the CU with the lid off, so we can see if it's a bodge or not.

I know - didn't take one - wish I did though

- - - Updated - - -

Why has the original contractor not been asked to this if it's a new build?


Original contractor subbed it to this Electrician!
 
by my rough calc. 16mm will handle 46A over a 50m length, giving a VD of 3% . what's the problem?
 
So you are saying only 3 cores of the SWA connected into the switch?

Does the 16mm suffer volt drop outside of the permitted in BS7671

What regs for SWA buried has to have a earthed sheath? TT on a outhouse, all they have done is extended the PME zone. Perfectly acceptable. Have you proven the metal pipework is a extraneous conductive part?

Ok so bad design on the showers.
 
this is a thread that needs a pic of the CU with the lid off, so we can see if it's a bodge or not.

2013-11-19 23.15.15.jpg

It was very similar condition to this one just bigger - 21Way MK CU - Split Load


This picture is taken of one I attended for British Gas Home Assistance
 
Originally Posted by Dillb No labels- hardly going too do any harm to anyone is it
TAils not terminated properly- so the rest of the live parts in the DB are all fully enclosed?
Tails not in properly - and not cut tidy - only 3 cores connected!
16mm SWA- What problem here?
50m Run - Preferably 25mm would have been better to avoid voltage drop! ....Better maybe, but that's not saying it doesn't comply!!
SWA Not earthed- Is the SWA used as a CPC? or is it run where it needs to earthed?
SWA Buried underground Is, or has the SWA been earthed at one end only ''outgoing end''??
PME- DNO responsibility? Although no problem with extending it
Regs State this must be TT .....REALLY THINK AGAIN!! Better still name that Reg?? lol!!
50 MCB- sounds like it is doing its job properly
RCD Discrimination ...Not actually against any regulation
3 showers- No problem here
if 2 Showers Running - MCB Tripps - 4 Bedrooms for all family members - usual situation for this customer .....Is this a Granny flat or a 4 bed house, ... make you're mind up??
No bonding- are there any extraneous conductive parts?
All Pipework is metal .....internal maybe, but what of the pipes entering the property, these day's plumbers tend to use plastic for everything??
 
So you are saying only 3 cores of the SWA connected into the switch?

Does the 16mm suffer volt drop outside of the permitted in BS7671

What regs for SWA buried has to have a earthed sheath? TT on a outhouse, all they have done is extended the PME zone. Perfectly acceptable. Have you proven the metal pipework is a extraneous conductive part?

Ok so bad design on the showers.

This building is 50m away from the main house! The Pipework is connected directly to a well!
You cant just extend a PME supply in this means - trying to find Reg now
 
One last time, i am repeating myself here. Is the metal work a extraneous conductive part? have you tested to prove it one way or the other?

Yes I have!

Ze between 100 and 200 ohms - acting as an earthrod


in regards to SWA - Armour is jsut cut and tapped at both ends - no glands
Inner insulation just passing through a 20mm hole in Iso in Main House - no supporting clamps - no earthing clamps
In House SWA is cut - only earth Conductor over 10mm is the 3rd core of SWA


2 x 30mA RCDs in Series
 
So you livened the house up without the main earth being connected?

What was your IR result when you tested between the main incoming earth and the metal work?

- - - Updated - - -

Yo have left lots of information out of you OP.
 
So you livened the house up without the main earth being connected?

What was your IR result when you tested between the main incoming earth and the metal work?

- - - Updated - - -

Yo have left lots of information out of you OP.


Like I said I went in to change Main Switch
Main Earth is connected via 3rd Core in SWA - its the Armor at Fault
Didn't IR - Installation Isolated and advised to get an electrician to repair work

Part of the MK contract is Im not allowed to offer my services to do work for these customers

Property owner is a retired Electrician (15th Regs) he had not looked in the CU ever
Nor had he checked any work - he relied on the Electrician being qualified and registered

I know i left lots out on my OP - sorry

Wish I had taken Pictures now! - Hind Sight is wonderful

- - - Updated - - -

I have a feeling the OP may have been registered before under a different name.

Never only this name sorry to disappoint you Dillb
 

Reply to Non Registered Spark wiring NewBuild in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock