I was speaking with a colleague who was confused about a circuit design that doesn't offer much selectivity.

A sub main is being fed via a SWA to a 63A commando style outlet which is to be used for temporary set ups (shows, Marquess etc).

The circuit is protected at circuit origin via a 30ma RCBO. All events that are plugged in use our little temporary boards which are movable. These temp boards have a little C/U with 4 circuits each. All circuits are again 30ma RCBO's.

My colleague was concerned that in the event of a earth fault on a circuit, there is no selectivity on which RCBO would trip. It would be a nuisance if the RCBO supplying the 63A outlet was to trip. I suggested possibly a time delayed RCBO at the circuit origin, however under the 18th all outlets up to 63A require 30ma rcd protection and I'm pretty sure you can't get a time delayed 30ma RCBO.

Any advice?
 
The only logical solution is to complete a risk assessment to omit RCD protection for the circuit.

True. And in all fairness, there is nothing to say an SWA needs Rcd protection.
 
True. And in all fairness, there is nothing to say an SWA needs Rcd protection.

As Strima says document a RA. Insisting all circuits plugged into the commando socket must be RCD protected and possible having it labelled as such would be sensible mitigating examples.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

gazdkw82

Arms
~
Joined
Location
leicester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Numerous RCD's, selectivity
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
5

Thread Tags

Tags Tags
rcd rcd's

Advert

Thread statistics

Created
gazdkw82,
Last reply from
Strima,
Replies
5
Views
2,968

Advert