Looking for a little advice.
I was speaking with a colleague who was confused about a circuit design that doesn't offer much selectivity.
A sub main is being fed via a SWA to a 63A commando style outlet which is to be used for temporary set ups (shows, Marquess etc).
The circuit is protected at circuit origin via a 30ma RCBO. All events that are plugged in use our little temporary boards which are movable. These temp boards have a little C/U with 4 circuits each. All circuits are again 30ma RCBO's.
My colleague was concerned that in the event of a earth fault on a circuit, there is no selectivity on which RCBO would trip. It would be a nuisance if the RCBO supplying the 63A outlet was to trip. I suggested possibly a time delayed RCBO at the circuit origin, however under the 18th all outlets up to 63A require 30ma rcd protection and I'm pretty sure you can't get a time delayed 30ma RCBO.
Any advice?
I was speaking with a colleague who was confused about a circuit design that doesn't offer much selectivity.
A sub main is being fed via a SWA to a 63A commando style outlet which is to be used for temporary set ups (shows, Marquess etc).
The circuit is protected at circuit origin via a 30ma RCBO. All events that are plugged in use our little temporary boards which are movable. These temp boards have a little C/U with 4 circuits each. All circuits are again 30ma RCBO's.
My colleague was concerned that in the event of a earth fault on a circuit, there is no selectivity on which RCBO would trip. It would be a nuisance if the RCBO supplying the 63A outlet was to trip. I suggested possibly a time delayed RCBO at the circuit origin, however under the 18th all outlets up to 63A require 30ma rcd protection and I'm pretty sure you can't get a time delayed 30ma RCBO.
Any advice?