martinsayer81

hi guys,

just a quick one, what zones can you fit a pull switch in a bathroom?

i have to fit a shower-light-fan combo above a bath that has a shower in it, can i fit the pull switch in the ceiling above the bath at the opposite end to the shower? This way it makes it obvious that the pull switch in the bath is for the fan,

and one other thing, what do they mean by an 'insulated' pull cord? do they mean a plastic pull cord?

cheers guys
 
What height is ceiling ?
Above ( i think ) 2.25 mtr no zones , but i wouldnt fit it directly above the bath / shower anyway , just to the side would be ok.
 
Yep, only SELV switches can be IN the zones, I think the insulated pullcord is "not a metal or conductive" pull cord.
 
ceiling height is 2.4M from floor level,so its outside the zones but when standing in the bath i can touch the ceiling!
 
plus the bathroom is quite small and the pullcord would look silly in the middle of the ceiling, plus there is already a pullcord just as you come into the bathroom for the other ceiling lights..
 
ceiling height is 2.4M from floor level,so its outside the zones but when standing in the bath i can touch the ceiling!

If it's at 2.4M then it is outside zones. Simple. If it is a piece of string, as is the norm, then it is insulated as far as the regs are concerned.
If you personally think that it could be sprayed then you can make the decision to move it further away.
 
wouldnt it look a bit cluttered with 2 pullcords side by side, and i think it would get confusing to guests as to with cord is for the lights, i want it to look good and be safe at the same time.
 
I always like to get the customer involved. Work out yourself where you think the pullcord is safe, then give the customer a few options. They will choose exactly where they think it looks best out of your suggestions and everyone is happy. Nothing worse than doing something you think is right, only to have an unhappy customer say "Oh, I don't want it there".
 
Went to a house today with three pull cords in the bathroom. One for the light, one for the shower, one for the fan. Cats would have a great time in there!!! :kittykay:
 
  • Like
Reactions: 3 people
Why not loop it off the existing lights?
One thing to bear in mind is just because it is outside of zones doesn't necessarily mean that it will be suitable for the location, as the installer you make the decision if it is fit for the external influences.
 
Why not loop it off the existing lights?
One thing to bear in mind is just because it is outside of zones doesn't necessarily mean that it will be suitable for the location, as the installer you make the decision if it is fit for the external influences.

thought it might be a nuisance if the fan kicked in when someone just wanted to use the loo late at night, when others are asleep!
 
Normally shower lights utilize an in line fan, my findings are they run quite quietly, but see your thinking. I'd probably still loop off existing though. :>
 
Went to a house today with three pull cords in the bathroom. One for the light, one for the shower, one for the fan. Cats would have a great time in there!!! :kittykay:

Thats what I like to call Kelp forest wiring
 
  • Like
Reactions: 1 person
Just had to google kelp forests. They are amazing. Thanks for bringing them to my attention. Oooppps off topic!!!!! :teeth_smile:
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
pull switch
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
18

Advert

Thread statistics

Created
martinsayer81,
Last reply from
Air Conditioner,
Replies
18
Views
2,583

Advert