So the house had a few probs before you changed the board.....Alarm bells should have rung then.EICR was prob ok but you should have put in writing that any remedial work that needed to be done after board change would be down to them to cover cost of investigation and remedial work
 
  • Like
Reactions: Midwest
Hi - if I’ve understood correctly it’s just this one circuit with the one transformer that sometimes trips? - other than changing the RCBO as already suggested you could perhaps also :

- confirm from the board the circuit has “excellent“ continuity (with the transformer primary bypassed) and insulation resistance.

- see if the fault moves with the transformer.

-replace the switch, as it’s not impossible that contact bounce is annoying the RCBO somehow ...
 
There's your answer then, a D type is most unusual and probably non compliant in a lot of domestic situations, I expect the new RCBO serving the kitchen lights will have a 'B' tripping curve, if the customer doesn't agree to new LED lights a C type 10a RCBO might do the trick.
[automerge]1584050062[/automerge]
The D type MCBs were originally fitted to counteract the high inrush current and nuisance tripping with the old toroidal transformers I expect.
Why would a type D 'probably be non compliant in a lot of domestic situations'?
If the measured Zs is satisfactory.....and anyway the OP stated there was originally an RCD main switch which largely negates any OCPD Zs issues.
 
  • Agree
Reactions: MJPD29
Why would a type D 'probably be non compliant in a lot of domestic situations'?
If the measured Zs is satisfactory.....and anyway the OP stated there was originally an RCD main switch which largely negates any OCPD Zs issues.

I knew there would be at least one picking up on that, I was referring to existing installations where there may not be RCD protection on the lighting,and the measured Zs could be unsatisfactory.How often have you seen type D MCBs in domestic installations ?
 
  • Like
Reactions: SparkyChick
I think it’s fine to offer the option of replacing the ELV lights but I’d be making it clear that it is just a good idea and not a necessity. I would be changing the B type RCBO for a C type free of charge if they chose not to change to GU10’s.
 
Bit of a stab in the dark here. I have encountered tripping on RCD where there is two way switching due to the way the 3 core was connected. By changing the cores around at the switches the RCD tripping stopped due to the "centre" (for want of a better description) cable being adjacent to the cpc no longer. You did seem to mention testing the switches both ways. Sorry if I have misunderstood, but I took that as there is two way switching in the kitchen?
 
Hardly ever, doesn't mean they are likely to be non compliant though.
I would say a 6A D type MCB or RCBO would have a 50% (approx) chance of being non compliant in a domestic situation as the Zs would have to be max 1.46Ω (TT).
I would say a 32A D type MCB or RCBO would have a 98% (approx) chance of being non compliant in a domestic situation as max Zs is 0.28Ω (TT).

My aspergery brain starts overheating when the word 'likely' is used as it is so subjective! It doesn't mean anything in this scenario. Even my approximations above are ridiculous as they are only ever so slightly less subjective.
It's a bit like that old 80's film 'war games' when the computer tries to find a winner in nuclear war and breaks down due to infinite 'no win' outcomes.

I will now stop drinking coffee.
 
I would say a 6A D type MCB or RCBO would have a 50% (approx) chance of being non compliant in a domestic situation as the Zs would have to be max 1.46Ω (TT).
I would say a 32A D type MCB or RCBO would have a 98% (approx) chance of being non compliant in a domestic situation as max Zs is 0.28Ω (TT).

My aspergery brain starts overheating when the word 'likely' is used as it is so subjective! It doesn't mean anything in this scenario. Even my approximations above are ridiculous as they are only ever so slightly less subjective.
It's a bit like that old 80's film 'war games' when the computer tries to find a winner in nuclear war and breaks down due to infinite 'no win' outcomes.

I will now stop drinking coffee.
I assume you mean TN....not TT? Any rating of type D would have a 100% chance of being compliant in a correctly designed TT.
I agree on a TN in many existing situations a device exceeding 6a may be non compliant, but in new additions, alterations and new installations in domestics any rating of a type D mcb is probably 100% likely to comply because virtually all circuits will have RCD protection, and an RCD is a permitted means of earth fault protection. RCD's are not only for additional protection, something that is often overlooked.
 
And now you're saying pretty much what I was getting at, bottom line is that a type D is not a good design choice for a new domestic install.
 
And now you're saying pretty much what I was getting at, bottom line is that a type D is not a good design choice for a new domestic install.
But that doesn't make it non compliant. Sorry but I get irritated by this, I've even heard talk in the wholesalers that only type B is permitted in domestics. That's how these phantom regs come about
 
When I did CU changes, they we’re mostly simple ones, never did an EICR before, but soo learnt to do some testing after my quote was approved and before taking the old one off the wall.

However in this instance I’m not sure if an EICR would of discovered the fault? Albeit, the reasoning behind the change, would of been cause for concern.

Hope OP has something in his T&C’s about remedial work, with CU changes.
 
  • Like
Reactions: radiohead
Why not swap the kitchen transformer with one of the other identical units and see if the fault moves.
 
Well after ordering a C Type RCBO from my local stockist, i thought id temporarily swap the B Type with an MCB so it wouldn't keep tripping now the husband has completely denied any conversation with his wife over the extra cost of replacing the downlight with GU10's, he's more than happy for me to replace them tomorrow I wonder if over the weekend he's had his ear bent so many times about the cost he wants to keep her in doors quiet!!!!
 
  • Like
Reactions: DPG and Midwest

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Bury

Thread Information

Title
RCBO intermittent tripping advise??
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
36

Advert

Thread statistics

Created
leebut,
Last reply from
leebut,
Replies
36
Views
10,545

Advert