I would say a 6A D type MCB or RCBO would have a 50% (approx) chance of being non compliant in a domestic situation as the Zs would have to be max 1.46Ω (TT).
I would say a 32A D type MCB or RCBO would have a 98% (approx) chance of being non compliant in a domestic situation as max Zs is 0.28Ω (TT).

My aspergery brain starts overheating when the word 'likely' is used as it is so subjective! It doesn't mean anything in this scenario. Even my approximations above are ridiculous as they are only ever so slightly less subjective.
It's a bit like that old 80's film 'war games' when the computer tries to find a winner in nuclear war and breaks down due to infinite 'no win' outcomes.

I will now stop drinking coffee.
I assume you mean TN....not TT? Any rating of type D would have a 100% chance of being compliant in a correctly designed TT.
I agree on a TN in many existing situations a device exceeding 6a may be non compliant, but in new additions, alterations and new installations in domestics any rating of a type D mcb is probably 100% likely to comply because virtually all circuits will have RCD protection, and an RCD is a permitted means of earth fault protection. RCD's are not only for additional protection, something that is often overlooked.
 
And now you're saying pretty much what I was getting at, bottom line is that a type D is not a good design choice for a new domestic install.
 
And now you're saying pretty much what I was getting at, bottom line is that a type D is not a good design choice for a new domestic install.
But that doesn't make it non compliant. Sorry but I get irritated by this, I've even heard talk in the wholesalers that only type B is permitted in domestics. That's how these phantom regs come about
 
When I did CU changes, they we’re mostly simple ones, never did an EICR before, but soo learnt to do some testing after my quote was approved and before taking the old one off the wall.

However in this instance I’m not sure if an EICR would of discovered the fault? Albeit, the reasoning behind the change, would of been cause for concern.

Hope OP has something in his T&C’s about remedial work, with CU changes.
 
Well after ordering a C Type RCBO from my local stockist, i thought id temporarily swap the B Type with an MCB so it wouldn't keep tripping now the husband has completely denied any conversation with his wife over the extra cost of replacing the downlight with GU10's, he's more than happy for me to replace them tomorrow I wonder if over the weekend he's had his ear bent so many times about the cost he wants to keep her in doors quiet!!!!
 

Reply to RCBO intermittent tripping advise?? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Wondering if you could offer some advice please. I carried out a small outdoor lighting project today at a commercial property. 4 lights...
Replies
5
Views
945
I have an issue with a home lighting circuit 6A RCBO provides power to 13 bulbs which randomly keeps tripping, when I say randomly it keeps...
Replies
8
Views
3K
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
763
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Quite old main switch RCD, it occasionally trips (every day or two), then won't turn on until all breakers are off. Ramp test at time of testing...
Replies
40
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock