Hi Guys
Just installed a RCBO board to replace an old Wylex consumer unit that had Bs60898 MCB's fitted and an RCD main switch customer supposedly hadn't had problems in the past (not quite sure thats now true) when I carried out the EICR I found a problem on the outside garden lights, so until the summer I've disconnected the garden lights circuit so all should be good.
The house is 25 years old and has minimal work carried out on it so no DIY Dave stuff, I finished fitting the board yesterday and went back today to install some outside wall lights but had issues all day with the kitchen lights tripping the RCBO every so often when the light switch is operated (but not every time) the kitchen, utility and lounge are all on the same circuit, only the kitchen lights trips the RCBO, question is has anyone had issues in the past with Low voltage downlighter's supplied by one large transformer tripping the RCBO I disconnected the transformer prior to the IR testing which came back almost perfect with the switches operated both ways etc.
Refitted the transformer and its tripping spent ages on this today, I've advised customer I think the Transformer is on its way out and recommended I install new downlight with GU10 LED lamps to replace the MR16 Halogens, everything was fine with that idea until husband came home and doesn't want to spend any more money without knowing this is going to cure the issue.
Anyone had anything similar??
This could simply be high inrush current being drawn by the transformer causing the overcurrent part of the RCBO to operate.
Was the previous MCB that covered these lights a 'C' tripping curve or perhaps 10a rated by any chance ?
Transformer with halogens? If the rcbo always trips when this circuit is turned on, then 100% the tranny.
Is it 25 year old same as house? I’d say it’s reached it’s expiry date.
For the cost of a few new LED downlights, the less heat generated and power consumption, it’s a no brainer
Hi Dave
majority of the lighting circuits in the CU were D10 Wylex (PSB 10D) MCB apart from two small circuits that had B6 (NSB06)
lee
Changing to LED lamps makes a lot of sense in any case, lower power consumption and much longer life.
You might want to double-check the insulation to see it is not L-N fault either, but if nothing has changed since the inspection then the previous suggestion on the over-current tripping sounds plausible. Also double check the isolation of circuit neutrals, but a stupid "borrowed neutral" would likely see another RCBO trip occasionally instead.
Finally if you have a sensitive enough clamp ammeter (looks on desk, sees DiLOG DL6518 sitting there) you could check the residual current by putting L&N through it to see if there is anything leaky when running that gets anywhere close to 15mA.
Hi mate
yeah the house has a few of these old drum type Trannys fitted this one has six outlets going to the downlight etc, I explained this to the customer she was happy for me to do work then texts me saying husband doesn't want to spend £200ish to rectify this nuisance tripping unless I can guarantee its the problem (he's just bought a brand new Porsche so probably skint)
There's your answer then, a D type is most unusual and probably non compliant in a lot of domestic situations, I expect the new RCBO serving the kitchen lights will have a 'B' tripping curve, if the customer doesn't agree to new LED lights a C type 10a RCBO might do the trick.
[automerge]1584050062[/automerge]
The D type MCBs were originally fitted to counteract the high inrush current and nuisance tripping with the old toroidal transformers I expect.
Finally if you have a sensitive enough clamp ammeter (looks on dsek, sees DiLOG DL6518 sitting there) you could check the residual current by putting L&N through it to see if there is anything leaky when running that gets anywhere close to 15mA.
I've got an earth leakage clamp meter didn't try it because I was convinced it was the Tranny anyway, I think its a no brainer to change fittings to GU10 and LED lamps
Missed that, but that would appear to explain everything!
Should have seen it coming though, as in the past (not domestic wiring) we put in NTC thermistors on the toroid supply to cut the switch-on surge and increase the life of switching relays. They were burning out after a few k operations and not the 50k that was needed.
Hi Dave
thanks for the info and advice, to me the D10 MCB (there are 4 of them two seeing the light circuits and two for the external flood lights around the house) looked to have been changed at some point from the original NSB breakers that makes up the rest of the board so your probably right about changing to a C type RCBO, I thought the PSB breakers were for non domestic board and three phase boards!!
It's a no brainer to expect you to correct your error at your own cost, the customer shouldn't have to pay any extra because you have fitted protective devices which are unsuitable for the installed equipment.
[automerge]1584051227[/automerge]
Why is that? A toroidal transformer can be expected to last longer than that without issue.
Hi mate
If he can afford the Porsche he can afford to spend a few quid making his home safer. I despise people like that. But if the circuit has tested ok and there are no faults then I agree with the advice to change it to a type C. Cant imagine earth leakage being 30ma.
Not just the Porsche, theres a Mercedes, a Mini and BMW RV on the drive wonder how he affords all of them and don't want to spend a few quid on his house Typical accountant!!
Yes he can afford to make his home safer, and having the CU replaced is doing exactly that.
However he shouldn't have to pay for the replacement of installed equipment just because the person who installed the CU has fitted the wrong protective device for that equipment.
[automerge]1584051605[/automerge]
He affords them by not paying out for unnecessary work to be done on his house.