[/QUOTE]
He affords them by not paying out for unnecessary work to be done on his house.
[/QUOTE]
Nooo, but it helps a bit to pay the fuel bill.....
 
He affords them by not paying out for unnecessary work to be done on his house.
[/QUOTE]
Nooo, but it helps a bit to pay the fuel bill.....
[/QUOTE]
He's an accountant so probably doesn't pay the taxman very much money each year
 
So the house had a few probs before you changed the board.....Alarm bells should have rung then.EICR was prob ok but you should have put in writing that any remedial work that needed to be done after board change would be down to them to cover cost of investigation and remedial work
 
Hi - if I’ve understood correctly it’s just this one circuit with the one transformer that sometimes trips? - other than changing the RCBO as already suggested you could perhaps also :

- confirm from the board the circuit has “excellent“ continuity (with the transformer primary bypassed) and insulation resistance.

- see if the fault moves with the transformer.

-replace the switch, as it’s not impossible that contact bounce is annoying the RCBO somehow ...
 
There's your answer then, a D type is most unusual and probably non compliant in a lot of domestic situations, I expect the new RCBO serving the kitchen lights will have a 'B' tripping curve, if the customer doesn't agree to new LED lights a C type 10a RCBO might do the trick.
[automerge]1584050062[/automerge]
The D type MCBs were originally fitted to counteract the high inrush current and nuisance tripping with the old toroidal transformers I expect.
Why would a type D 'probably be non compliant in a lot of domestic situations'?
If the measured Zs is satisfactory.....and anyway the OP stated there was originally an RCD main switch which largely negates any OCPD Zs issues.
 
Why would a type D 'probably be non compliant in a lot of domestic situations'?
If the measured Zs is satisfactory.....and anyway the OP stated there was originally an RCD main switch which largely negates any OCPD Zs issues.

I knew there would be at least one picking up on that, I was referring to existing installations where there may not be RCD protection on the lighting,and the measured Zs could be unsatisfactory.How often have you seen type D MCBs in domestic installations ?
 
I think it’s fine to offer the option of replacing the ELV lights but I’d be making it clear that it is just a good idea and not a necessity. I would be changing the B type RCBO for a C type free of charge if they chose not to change to GU10’s.
 
Bit of a stab in the dark here. I have encountered tripping on RCD where there is two way switching due to the way the 3 core was connected. By changing the cores around at the switches the RCD tripping stopped due to the "centre" (for want of a better description) cable being adjacent to the cpc no longer. You did seem to mention testing the switches both ways. Sorry if I have misunderstood, but I took that as there is two way switching in the kitchen?
 
Hardly ever, doesn't mean they are likely to be non compliant though.
I would say a 6A D type MCB or RCBO would have a 50% (approx) chance of being non compliant in a domestic situation as the Zs would have to be max 1.46Ω (TT).
I would say a 32A D type MCB or RCBO would have a 98% (approx) chance of being non compliant in a domestic situation as max Zs is 0.28Ω (TT).

My aspergery brain starts overheating when the word 'likely' is used as it is so subjective! It doesn't mean anything in this scenario. Even my approximations above are ridiculous as they are only ever so slightly less subjective.
It's a bit like that old 80's film 'war games' when the computer tries to find a winner in nuclear war and breaks down due to infinite 'no win' outcomes.

I will now stop drinking coffee.
 

Reply to RCBO intermittent tripping advise?? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Wondering if you could offer some advice please. I carried out a small outdoor lighting project today at a commercial property. 4 lights...
Replies
5
Views
945
I have an issue with a home lighting circuit 6A RCBO provides power to 13 bulbs which randomly keeps tripping, when I say randomly it keeps...
Replies
8
Views
3K
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
763
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
2K
Quite old main switch RCD, it occasionally trips (every day or two), then won't turn on until all breakers are off. Ramp test at time of testing...
Replies
40
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock