pads

The wiring in the house is split into separate circuits each with their own RCBO for
3 for lighting (separate for ground floor; upper floor; and basement)
3 for power (again as above)
1 for cooker
1 for shower
2 for fridge/freezers

The problem exists only on the ground floor power circuit.
Whenever the vacuum (two core) is switched on in any socket, the RCBO trips. It's not the vacuum as it dos not happen on the upper floor. I have even tried an angle grinder- thinking maybe induction issues - but it does no trip.

Occasionally the circuit trips on its own, or if the computer is switched on.

I've checked all the sockets for damaged or trapped wiring, but nothing found.

Does anyone have any suggestions please.

Thanks
Peter
 
Bloody amateurs! It's obviously a fault on the kettle, everyone puts the kettle on to boil while they're doing a bit of vacuuming and no one ever suspects their good friend the kettle because it never lets them down.
Well, think again because it's no friend. It's there in the corner just waiting to scald you and one day it'll take its' chance.
Don't say I didn't warn you!
 
What sort of spark were you?
one of these maybe:

metal-welding-sparks-22364069.jpg
 
To those who are saying 'faulty appliance'. It was initially thought to be vacuum, but as I said later --

I have unplugged or switched off (where via switched spur outlet - DP) all items on the same RCBO. And the RCBO stays on for about 2 mins or little more then trips. Without doing anything. (Yes even the boiler and kettle are off)

So its not the kettle or the vac.

I'll do some more testing in the morning.

Peter
 
Personally I don't think you deserved some of the responses you got.

If you've been out of the game for a few years you probably don't have your fault finding head on.

You have to bear in mind that a lot of new posters on here are DIY or chancers and there are a lot of folks sick of it.

As has been said before if you are still struggling with it after testing post up what tests and results and then you will most likely get some helpful responses.

There will probably still be some sarcy remarks but that is the nature of this forum.
 
Have you tried switching/swapping the upstairs sockets RCBO for the downstairs sockets RCBO?? RCD devices as a whole, are not known for being overly reliable. So if after conducting any further testing without results, try swapping over the two RCBO's....
 
ramp test the RCBO with circuits connected but loads unplugged. note reading. then disconnect circuit/s from RCBO and ramp again.
 
OK some observations and test results.
Observations -
during the evening last night the RCBO kept tripping with nothing plugged in (or DP off)
but during the night, I put the boiler on and wife put the dishwasher on - but the RCBO stayed on all night!!!

Tests
1 - the ring is complete (both L & N) - zero ohms.
2 - neither L nor N connect to any other circuit on the CU
3 - L-E, and N-E, and L-N all measure 38M for the ring.
4 - connected L&N across all the CU and they measure 34M between LN-E.

The max age of the wiring in the house is about 28 years
 
Have you tried switching/swapping the upstairs sockets RCBO for the downstairs sockets RCBO?? RCD devices as a whole, are not known for being overly reliable. So if after conducting any further testing without results, try swapping over the two RCBO's....

I find a nail to be a good substitute for an RCBO that keeps tripping.

You may have to cut it and bend it a bit to make it fit, but fit it will - with a bit of persuasion from a lump hammer.
 
OK some observations and test results.

Measured trip times for the RCBO?

If you don't have the wherewithal to test that, swap the RCBO with another RCBO on the board and see if the problem follows the RCBO to the new circuit (=problem is RCBO) or stays with the circuit (=problem is circuit).
 
OK some observations and test results.
Observations -
during the evening last night the RCBO kept tripping with nothing plugged in (or DP off)
but during the night, I put the boiler on and wife put the dishwasher on - but the RCBO stayed on all night!!!

Tests
1 - the ring is complete (both L & N) - zero ohms.
2 - neither L nor N connect to any other circuit on the CU
3 - L-E, and N-E, and L-N all measure 38M for the ring.
4 - connected L&N across all the CU and they measure 34M between LN-E.

The max age of the wiring in the house is about 28 years
When was the rcbo board fitted?
 
In reply to some questions -
a) RCBO fitted within last 3 months
b) My multi-meter has ranges from 20m >> zero ohms
c) My insulation tester goes up to 2000M

Further Testing Results
After the first set of tests, I discovered the burglar alarm was still plugged in !!
So re-tested and checked insulation for each circuit individually disconnecting from CU as tested.
Fuse--------Circuit--------------- LN------------NE------------LE
1 -----------Shower ----------- >2000 ------- >2000 ------ >2000
2 -----------1st Fl Light ------- >2000 -------- 134 --------->2000
3------------Gnd Light -------- >2000 -------- 149 --------->2000
4 -----------Base Light -------- >2000 ------- >2000 ------>2000
5 -----------1st Fl Ring --------- 1600 --------- 780 ----------1200
6 -----------Gnd Ring ------------ 390 ---------- 34 ----------- 420
7 -----------Base Ring ---------- 1170 ---------1100 -------- 1000
8 -----------Cooker ----------- >2000 ------- >2000 ------>2000
9 -----------Freezer ----------- >2000 ------- >2000 ------>2000
10 ----------Frid/Freezer ------ >2000 ------- >2000 ------>2000
.... All in M ohms
yes - I have swapped the RCBOs for gnd and 1st Floor - always gnd floor which trips.

The results above indicate the Gnd floor 'NE' is suspect - but cannot see anything. By the way all wiring is exposed in basement so didn't have to lift floor boards to visually inspect.
 
Last edited by a moderator:
agree that 34Meg. looks to be the likely culprit. i'd be looking in all accessories for a partially trapped cable or damp somewhere. with damp being favorite as the L-N and L-E are lower than other circuits.
 

Reply to RCBO keeps tripping - without explanation in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock