- Reaction score
- 2,046
Surely it won't have a chance to saturate the coil of the upstream RCD as the Type B in the unit itself will already have disconnected?The DC current passing back through the installation which is why the type B is selected can saturate the coil of the type AC, its rcd selection in part 5.
If your selecting a type B because there’s that level of DC then it stands to reason that any rcd upfront in series requires the same consideration.
If I were fitting an EV charger at a garage in a large property with TT earthing arrangement I would likely have problems fitting Type B only RCD's. I'd probably need an S type RCD for the distribution circuit to the garage and I've never seen a Type B, time delayed RCD yet? Maybe they do exist though..
I get that it's desirable to have all type B RCDs. Actually it's most desirable to only have 1 RCD in any circuit because of selectivity, but it doesn't mean you're going against regs if you don't do things this way?