So if you want to fit an EVSE on a TT supply with upfront S type you effectively can’t?
That's the conclusion I'm arriving at, if the charger requires Type B RCBO, and why I'd directed the question to Risteard. I figure he might have considered this possibility.

Edit: Just spotted @Ian1981 post, which seems to confirm this thought.

There doesn't yet appear to be a great selection of available 2 pole time delayed 100mA Type S RCCBs, with Type A characterisitcs and I'm surprised that Wylex haven't yet introduced a version of the widely used WRMT100/2. Currently the best priced and most widely available options appear to be those from CP Fusebox and Lewden.
 
Last edited:
Not that I have seen. Doepke have a good range of type B (at a price!) but none are delay ones to mk knowledge.

As best I can ascertain, they manufacture a couple of industrial Type B time delayed RCCBs, but nothing suitable for a typical domestic installation.

DFS4 B and DFL8 B
 
But how much?

I would consider anything more than a few mA to be a fault, as one would expect the system (even at 48V or whatever considered "safe") to have insulation resistance of hundreds of kohm to earth.

If the EV charger is OK for a 30mA type B RCD than it would have to be below 15mA normally, or it is in the trip region. And as above, I can't see that sort of level saturating any type A RCD, and not a 100mA (or above) type AC.

If you had it off a 30mA AC RCD/RCBO I would be a bit more concerned

But for playing with some type-AC RCD FCU recently they would trip on the type A waveform OK, just too low current in one direction, and a little slow in the other direction.

So for sure if you could have significant DC then you need type B, but upstream of that I can't see it causing difficulties for any that are going to be selective anyway (so 100mA or above TT incomers).
From my understanding A type are up to 6mA and F&B types are up to 10mA. Without knowing the manufacturers information I couldn't comment on how much leakage they have but some do stipulate B type RCDs so it must be a fairly high current they generate during normal use.
 
So if you want to fit an EVSE on a TT supply with upfront S type you effectively can’t?
You can. I did two recently for a well-known major courier company.

One was single phase and I replaced the Type AC S-type with a 300mA Type A S-type, along with a Type A 30mA for the EVSE - which had inbuilt 6mA DC leakage protection.

The other was three-phase so I replaced the Type AC with a four pole 300mA Type A S-type, and a four pole Type A 30mA for the EVSE (again with built-in 6mA DC leakage protection).
 
That's the conclusion I'm arriving at, if the charger requires Type B RCBO, and why I'd directed the question to Risteard. I figure he might have considered this possibility.

Edit: Just spotted @Ian1981 post, which seems to confirm this thought.

There doesn't yet appear to be a great selection of available 2 pole time delayed 100mA Type S RCCBs, with Type A characterisitcs and I'm surprised that Wylex haven't yet introduced a version of the widely used WRMT100/2. Currently the best priced and most widely available options appear to be those from CP Fusebox and Lewden.
Sorry, was working until 8:30p.m. tonight so only seeing your post now. I haven't come across an RCBO with a Type B RCD characteristic (though they may exist). Any Type B RCD I have fitted has been an RCCB.

If a Type B RCD is needed then any upstream RCD will need to be Type B also. If Type A, then any upstream will need to be at least Type A.

You shouldn't have any issue finding a double pole Type A S-type RCCB - they are widely available.
 
Sorry, was working until 8:30p.m. tonight so only seeing your post now. I haven't come across an RCBO with a Type B RCD characteristic (though they may exist). Any Type B RCD I have fitted has been an RCCB.

If a Type B RCD is needed then any upstream RCD will need to be Type B also. If Type A, then any upstream will need to be at least Type A.

You shouldn't have any issue finding a double pole Type A S-type RCCB - they are widely available.

No worries about the time and I appreciate the response - it was purely hypothetical and came to mind after Type B requirement for certain chargers was introduced in post #17.
 
Further to this discussion here:
 

Reply to RCD requirements for TT? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
741
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
551
Hello! I've been racking my brain this evening about some RCD selections. I've been doing some work for a solar installer, and they've asked me...
Replies
5
Views
913
Hi Guys, Long time member and not a regular user here. I do pop in here when the odd unknown pop's up and unable to locate an electrical dilemma...
Replies
4
Views
861

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock