Just carrying out an EICR for a medical centre and want to get this right regarding section 710.
Most of the rooms are purely consultation rooms for the GPs but there is one treatment room where they carry out minor procedures. I think this makes it a group 1 location.
There are 2 things I want to get peoples thoughts on before I complete the paperwork.
710.411.3.3 additional protection. I think this means all circuits below 63A within the room need to be on 30mA rcd
710.559 lumnaires and lighting installations says at least 2 different sources of supply shall be provided one of which connected to the supply for safety services.
Now this building doesn't have a supply for safety services like an essential supplies db or backup arrangement. Would I be correct in thinking that to comply I would have to split the lights onto 2 circuits even though there are only 4 lights in the room.
Also would you give these a code c3.
Opinions most welcome
Most of the rooms are purely consultation rooms for the GPs but there is one treatment room where they carry out minor procedures. I think this makes it a group 1 location.
There are 2 things I want to get peoples thoughts on before I complete the paperwork.
710.411.3.3 additional protection. I think this means all circuits below 63A within the room need to be on 30mA rcd
710.559 lumnaires and lighting installations says at least 2 different sources of supply shall be provided one of which connected to the supply for safety services.
Now this building doesn't have a supply for safety services like an essential supplies db or backup arrangement. Would I be correct in thinking that to comply I would have to split the lights onto 2 circuits even though there are only 4 lights in the room.
Also would you give these a code c3.
Opinions most welcome