Sunny explorer, Under settings/grid monitoring mine says Country standard G83/1
Hi wstevew
Interesting, under the same menu mine says "special setting". Do you log on to Sunny Explorer as user or something else? I mentioned this to the installers so they are going to check.
Thanks fro your help.
Motters
 
Yes that was as a user.

Earthstore is right they haven't set it up right. Quite common as they have to set the dials behind the black panel correctly. After 10hours it locks the setting and it can only be change with sunny explorer as installer and they.must have a grid guard code from SMA.
 
Hi All
Thanks for all your responses, system seems to be cured no after changing the country setting to G83/1. Last four days have seen 24 KWh a day generated so I`m quite happy with that.

Seems the installers have never had to change a country setting before.

Once again thanks for your help.

Cheers

Motters
 
Seems the installers have never had to change a country setting before.
that doesn't bode well, being as all sunny boy HF and TL inverters need the country code setting on installation.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Solar Panel Output cutting out
Prefix
N/A
Forum
Solar PV Forum | Solar Panels Forum
Start date
Last reply date
Replies
43

Advert

Thread statistics

Created
Motters,
Last reply from
Gavin A,
Replies
43
Views
12,375

Advert