Hi,

a recent PIR has picked up no RCD protection and no supplemantry bonding to pipe work.

Am i correct in saying if all circuits to bathroom are protected by RCD then supplementary bonding is not required?
 
couldn't you have put your last 3 questions in one thread? seen as though its all the same job?
 
Hi,

a recent PIR has picked up no RCD protection and no supplemantry bonding to pipe work.

Am i correct in saying if all circuits to bathroom are protected by RCD then supplementary bonding is not required?

Not quite true, it depends what type of installation you are talking about, SB is still required in a lot of cases.

If you are talking about domestic bathrooms, then all of these conditions need to be met to omit SB,

1) the final circuits meet the requirements for ADS
2) all final circuits in the location have additional protection by means of an RCD 30mA
3) all extraneous conductive parts of the location are effectively connected to the protective equipotential bonding (main protective bonds) to the MET
 
  • Like
Reactions: 5 people

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
supplementary bonding and rcd protection
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
5

Advert

Thread statistics

Created
paulthemagpie,
Last reply from
Octopus,
Replies
5
Views
2,206

Advert