Hi all,
I am currently planning on designing an installation for a conservatory to be fitted with lights, floor sockets, and underfloor heating. My plan was to take a 6mm T+E from the Hager consumer unit under the stairs, protected at 32A, which would then run above the ceiling of the room adjoining the conservatory. My plan was to bring the cable down the wall of this room and drill directly through into the conservatory and have a small consumer unit in there with RCBO's for lights, sockets, and underfloor heating. My dilemma is that as the distribution cable will be chased into the wall on its way to the conservatory, RCD protection at the source (under the stairs) would be required. This would then mean there would be two 30mA RCD's in series. I understand that RCD protection for the sub-main may be overcome by using steel conduit or SWA in the wall but I would have liked to avoid this if possible and wondered if it can somehow be done with a higher rating RCBO at the source like 100mA or a time-delayed RCD? The wall is only single brick thick so burying at a depth greater than 50mm also isn't an option.

Many thanks
 
For a rcd to sit above another it must have both a higher trip value, and a longer operating time, as when there is a fault there is likely to be a substantial current - 100, 200 or more amps, whatever the value it is likely to be well in excess of the trip setting 30mA or 100mA - so both devices will be tripping instantly ~10ms

Use armoured cable, or conduit, as with twin&e you must use 30mA no time delay.

Or use mcbs rather than rcbo and just accept an earth fault would trip the rcd in the main cu - just like any other rcd split board.
 
or you could feed the sub from a RCBO in the main CU, so a fault in the conservatory won't take out rest or part of house. all depends on the config. of the CU. if it's got a non -RCD way
 
You may be over engineering it. Depending on the house and layout of course.

As a similar scenario, my outbuilding has an upfront RCD at 30mA at the house CU, cabled and protected accordingly. In the outbuilding (or annex as its best described) is a CU with a main switch + MCB configuration, used purely for the distribution - it supplies annex sockets, UFH, conservatory sockets, lighting etc.

It's a layout that bothers some, as one RCD covers multiple circuits. However, in my layout it really is irrelevant. If the upfront RCD tripped, taking out my sockets, UFH and lighting, the layout of my house means thay the lighting from the main house easily lights enough of the annex up, for me to return to the main CU in safety. For extra cover, I have installed a discreet recessed emergency light near the annex CU.

Can your layout work in a way that allows the RCD to be upfront perhaps?
 

Reply to Upstream RCD's in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
724
Hi all, Grateful for your expertise regarding my confusion on the below. Context: French rural domestic property Single phase supply, TT...
Replies
12
Views
2K
I was wondering if someone might be able to help either confirm or change my understanding on the use of S-Type RCDs. I believe that they can be...
Replies
1
Views
637
Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
320
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock