I've been thinking about running a supply to my garage for a while, some sockets and lighting etc. the usual. Thinking of burying some SWA as I have some XLPE 2.5mm² three core knocking about into a CU from the house CU. It'll be around a 30-40 metre run but after apply a bit of diversity sticking it on a 20A MCB the voltage drop is far too high considering they'll be lighting on the new CU and that's before adding the voltage drop from the lighting circuit itself.

Any ideas? Or have I missed something? I could get a bigger cable but be a shame to not use it.
 
you are using the In of your OCPD as a value for current. be honest, how much are you likely to pull? go for a Ib of 10A and you VD will be OK.
 
you are using the In of your OCPD as a value for current. be honest, how much are you likely to pull? go for a Ib of 10A and you VD will be OK.
You're right! It will be pulling pittance for sure, forgot to use Ib instead of In. Thanks a bunch tel!
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
VD for Sub Main
Prefix
N/A
Forum
Electrical Course Trainees Only
Start date
Last reply date
Replies
2

Thread Tags

Advert

Thread statistics

Created
Spearmint,
Last reply from
Spearmint,
Replies
2
Views
78

Advert