Been to look at a fuseboard upgrade.


The house has a 3-phase cutout. One phase isn’t used, and the other two phases feed a single phase meter each. The house therefore has two single phase meters, each feeding an old wooden Wylex board.


One meter/board does lights, garage and a few sockets, the other does mostly sockets. Can’t see any obvious reason why it's set up like it is.


Can anyone see any issues with me getting one of the supply phases de-energised and installing a new consumer unit for the whole house, on one phase?


It’s big 6-7 bedroom house but the overall energy usage would be fine on one phase. They’ve got 2 8.5kW showers, a double oven and usual lights and sockets.


My only concern is that the DNO likes to balance loads between phases. Am I doing anything wrong by putting all the customer’s demand onto one phase?


I don’t know what size fuses are in the cut-out as it’s still sealed. And no, it's not economy 7 or anything like that.



Thanks in advance.
 
all you can do is speak to DNO.
 
Could it be in the distant past that the property was actually split into 2 properties, then converted back to 1?
 
Not really Murdoch due to the way the circuits are splitbetween boards. Mostly sockets on one,mostly lights on the other.
 
  • Like
Reactions: 1 person
Nope, couple of ring mains, but I’d be interested to know what you're thinking - old storage heater circuits?
 
Thanks for all the replies. I’ll speak to DNO as telectrix says. Jut annoying that I only get chance to look at these things on Saturdaywhen they’re shut!

 
Why do you want to have a phase removed?

I’d make use of both phases.

Is it a case of you don’t know how to?
 
Because the customer’s paying two standing charges and has to deal with separate electricity bills
 
Having 2 DB's across 2 phases is not a bad position to be in - unless they are being charged more for the supplies!

Unless they want to use Powerline adaptors!
 
  • Like
Reactions: 1 person
Because the customer’s paying two standing charges and has to deal with separate electricity bills

Get the customer to ask for a 3 phase meter to be fitted by the supplier
 
Historically more than likely had s/heaters in.
 
Simple explanation for this would be that they had a second phase connected at some point in time and didn't have a meter capable of working on the two phases with them on the day the board came to connect.

Just get the meter operator out to swap it for a single meter on the two phases, they won't then have to pay the two standing charges
 
Three phase meter, is an good idea, you don't need L3 but hey ho, one standing charge.
 
If you are upgrading the DB like you say in your Op then obviously the best option would be to have both meters upgraded to one 3phase meter, install a new 3phase DB and balance the load across all 3phases.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
why has house got two meters?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
18

Advert

Thread statistics

Created
sparkol,
Last reply from
Leesparkykent,
Replies
18
Views
2,072

Advert