Discuss Workshop power in the UK Electrical Forum area at ElectriciansForums.net
But in any event if you use the correct value of U0 it is less than 2kW.
The 2kW is only a nominal value at a nominal voltage, quoted by manufacturers as with voltage fluctuations or volt drop the output power could be less but could also be more if manufacturers base it on a nominal 230v and actual is 234volts!
But it's always been that way for resistive loads - they are quoted at a particular voltage or voltage range.
The correct voltage to use in calculations is 230, so loads should be evaluated on the basis of what they are at that voltage.
new electric oven installed which is 240v 2075w.
So it should be viewed as 1906W.
I don't think you'd get many takers for the view that a 1700W appliance should be put on a dedicated circuit as it would be over 2kW at 253V.
Agree but many Electricians want the rules and regulations in black and white, it wouldn't be to much to ask to point this out to the less educated newbies amongst our community would it?, maybe those that think they know it all will disagree. What do you think? I'm not including you in the know it all statement by the way.
Some counties have Regs imbedded in the law and their Regs are very specific about compliance with prison sentences for when it goes wrong. I was working in one such country when I took their Regs course and we were told at the time there were 4000+ electricians facing prosecution.
I sometimes wonder why folks get so worked up about the "2kW fixed load" thing.
We all know the RFC is quite robust and tolerant of most things and many houses have (or had) practically everything bar the lights & cooker on a single RFC. Quite often folks would have a couple of 3kW heaters and the usual washing machine, tumble dryer, etc, in use and no problems.
Putting significantly more than 13A on at a point on the RFC is getting in to suspect territory as you can't be sure of how well the currents in the two "legs" are going to balance, but we have few loads that come in to that area. Probably just wired-in cookers, heating showers, or an EV charger in recent year or two, and they would normally be on separate radials anyway.
The only odd one I can think of is the old immersion heater, less popular these days due to combi boilers and instant-heat showers, as they would typically be around 3kW and could be heating for an hour or more easily. So were they the motivation for saying fixed loads above 2kW, and not the 3kW of a 13A socket?
Also the argument for putting something on to a separate circuit goes beyond the basic aspect of circuit protection alone, there is also the "good engineering" aspect of minimising inconvenience/risk under fault conditions to allow the fault to be isolated with the least collateral damage. I guess a number of "fixed loads" come in to this sort of territory, especially water heaters, where you would want to be able to keep any faults from taking out all/half of the house socket outlets as well.
This is exactly why! The above may well work on a single RFC with no problems in practice, but if there's a 2kW+ fixed load as well, that will likely take it over the edge.
Reply to Workshop power in the UK Electrical Forum area at ElectriciansForums.net
Hi all, I have a log cabin in my garden. An electrician ran an armoured cable from my consumer unit to the log cabin and this terminates on the...
Some friends are setting up a metal workshop inside a shipping container, on site at a commercial building that rents out studios, workshop space...
Hi All, We have an old Country villa in Spain. The housing electrics were not good so the house recently has been completely re-wired to a good...
Hi I'm in need of some advice. First of all i'm not an electrician but do have an understanding of electrics as i come from an electronics...
