crow11

hi all just a quick question about the above title,go easy with me if i am missing something obvious here lol, why do you have to put zs at d/b on the eicr(got a copy of part p doctor and on his sample of schedule of test results he as put the ze figure in there and then put ze in brackets at the side of it,if you was to do a zs test at d/b do you just do it at the main switch line in with switch open and then obviously to main cpc bar in d/b, obviously you could expect to get a lower reading than the ze because of parallel paths, and the next 1 Ipf at d/b wouldn't this just be the same as the pfc you put down on the first page of the eicr so why do you have to put it down twice cheers
 
Your ze may not be at the board, maybe a scenario like fused isolator then to consumer unit, your ze would be at fused isolator and then you would have a db zs at the consumer unit
 
The reason why Zs is now required to be recorded on the schedule, is because recording a value that has already been recorded, is pointless.
Zs is very likely to be different from Ze.
Also this now allows the schedule to be used where there are multiple Dbs without having to alter the Ze to Zs.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
zs and Ipf at d/b on schedule of test results
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
2

Thread Tags

Advert

Thread statistics

Created
crow11,
Last reply from
Deleted member 26818,
Replies
2
Views
9,808

Advert