Heating has a dedicated rcbo feeding boiler, oil fed on S plan and seperate rcbo feeds immersion element for cylinder.What's the heating fed from?
Heating has a dedicated rcbo feeding boiler, oil fed on S plan and seperate rcbo feeds immersion element for cylinder.What's the heating fed from?
From bonding ? All the circuits on seperate pd'sParallel paths
No mate, all old stud and block walls very old granite block nightmare chasing it wasIs there metal stud work?
Various metal back boxes fixed to metal stud
Parallel paths through various connections and metal back boxes connected together via stud?
Driving me mad already and NICEIC assessor in 2 weeks !!Must be a very short loop you are reading, like a metre or so. You will laugh when you find it![]()
Just been sorting out a right mess during a house renovation and tests on newly installed ring final are r1 0.35
rn 0.35 & r2 was expecting around 0.58 but had consistently 0.00 Ohms.
MFT was zeroed again from scratch and was still giving a zero resistance reading
Almost all cable is new and IR tests all perfect. Any ideas ? Thanks
Need to test at a socket as it sounds like the cpcs are in contact either within or close to the CU.
I must admit I'm a little puzzled by you opening sentence ... "sorting out a right mess" - so are you testing an installation you didn't do?
If this new ring is your work, it should be a formality to resolve the issue.
Suppose you can null the wander lead, to get just the reading for r2. Depends on how far the lead has 'wander' round the house?]
Wouldn't be near the length as all ground floor & board in garage, lead us 50m so easy enough