Is there metal stud work?
Various metal back boxes fixed to metal stud
Parallel paths through various connections and metal back boxes connected together via stud?
Just been sorting out a right mess during a house renovation and tests on newly installed ring final are r1 0.35
rn 0.35 & r2 was expecting around 0.58 but had consistently 0.00 Ohms
MFT was zeroed again from scratch and was still giving a zero resistance reading
Almost all cable is new and IR tests all perfect. Any ideas ? Thanks
I must admit I'm a little puzzled by you opening sentence ... "sorting out a right mess" - so are you testing an installation you didn't do?
If this new ring is your work, it should be a formality to resolve the issue.
Need to test at a socket as it sounds like the cpcs are in contact either within or close to the CU.
Reactions: Soulsurfer
Wot about doing the r1+r2 test on each leg, like when your trying to find a break in a ring? Break the ring at the furthest socket, then test each leg? Just a suggestion, might be a pants idea?
i'd be going round with a wander lead on the cpc with the ends separated in the CU..and maybe also at mid-point.
Existing was a bad spider jointed mess have taken out almost all cables except one old leg which I couldn't get out so re-used & all rest is new cable.
Have a wander lead myself, but why bother making things difficult, when you have a perfectly good r1 to test your r2?
Suppose you can null the wander lead, to get just the reading for r2. Depends on how far the lead has 'wander' round the house?
Soulsurfer
Channel Islands
Business Name
M.B.S ELECTRICAL
Renovated house low r2 readings !
Soulsurfer,
HandySparks,