Hi all, I'm new here.
I have qualified back in 1990 and worked only a few years in the trade. Now I'm back and I find myself a bit "rusty" and in need of a bit of help...

I have to wire a complex of coldstores and I have to make a fuse boards for a part of them. I have 6no 10 amp MCBs, 2no 20 amp MCBs and 8no 20 amp RCBOs in it. Just a few lights and sockets circuits. I have no idea what's going to be plugged in and for how long, the client can supply single or three phase.
What size switch fuse do you think I should use?
Thanks in advance
 
300mm x450 mm nice bit of room to work in then. Haven’t a clue on the correct rating of the fuse tho would need more info for that
 
Where is my wand? I had one cuz I made it myself
 
If you don’t know what’s being connected or for how long the loads are on the circuits you won’t be able to apply any diversity to the load. You need to speak to the client as others have said.
Who decided on the protective devices and their ratings, how was this decided on? Surely you must have had some design spec.
 
Sounds like this task is well outside your remit.
 
  • Like
Reactions: DPG
Hi all, I'm new here.
I have qualified back in 1990 and worked only a few years in the trade. Now I'm back and I find myself a bit "rusty" and in need of a bit of help...

I have to wire a complex of coldstores and I have to make a fuse boards for a part of them. I have 6no 10 amp MCBs, 2no 20 amp MCBs and 8no 20 amp RCBOs in it. Just a few lights and sockets circuits. I have no idea what's going to be plugged in and for how long, the client can supply single or three phase.
What size switch fuse do you think I should use?
Thanks in advance
Are you registered with RECI?
 
Thanks for your comments guys, I have more information this morning.

I'm not registered with RECI, I'm employed by a company that builds coldstores and they only require my qualification to sign them off.

There are a total of 25 lights, 5 foot LEDs, they are only 63 w each. I'd like a separate MCB for every room. 6 rooms, 6no 6amp MCBs?

My employer says that the sockets are for general use and to go with the maximum rating to cover ourselves. There are from 4 to 8 in each room. 6 circuits, 6no 20 amp RCBOs? I might wire the ones with 8 sockets as a ring.

There are 2 spurs for hand driers, 2no 20 amp MCBs?

2no panasonic air conditioners, 2no 20 amp RCBOs or MCBs, not sure

Back in the days I use to wire the mains to a switchfuse in the consumer units, is that not the case anymore?

Thanks
 
You really shouldn't be undertaking the work if you're not confident in your own knowledge and competence because if something goes wrong you're responsible and you will have to justify everything and every decision you've made from the design, installation and testing. Asking here gives you no cover should YOU cock something up.
 
  • Agree
Reactions: DPG and Pete999
You really shouldn't be undertaking the work if you're not confident in your own knowledge and competence because if something goes wrong you're responsible and you will have to justify everything and every decision you've made from the design, installation and testing. Asking here gives you no cover should YOU cock something up.

I'm sure there are times when you are not sure about things right?
Usually these coldstores are straight forward to wire and I have no problem with them. Sometimes we get the odd job and I can't say to my boss that I'm not doing it...
Do you think my guess on the breakers is not right?
 
If I'm unsure of anything I refer back to the relevant legislation I don't go on forums with a vague outline of proposed works to seek confirmation. You should have all the correct design and cable calcs for the installation and that should provide you with all the info you need. If you don't.....Well what are you playing at
 
If I'm unsure of anything I refer back to the relevant legislation I don't go on forums with a vague outline of proposed works to seek confirmation. You should have all the correct design and cable calcs for the installation and that should provide you with all the info you need. If you don't.....Well what are you playing at

I have no choice and I have to do the job.
Unfortunately I don't know as much as you about the trade but it is what it is... I can't change that.

I don't think my choice of breakers is far from what it should be, you still haven't express an opinion about that.
If you have no intention of helping, you don't have to keep replying otherwise we will be both wasting our time to get anywhere.

Thanks for your comments so far
 
My employer says that the sockets are for general use and to go with the maximum rating to cover ourselves. There are from 4 to 8 in each room. 6 circuits, 6no 20 amp RCBOs?

So are you going with the 'maximum rating' or 20A??

I might wire the ones with 8 sockets as a ring

Either a Ring Main (it's Friday and that's going to annoy quite a few people) or a Radial.
 
So are you going with the 'maximum rating' or 20A??


Either a Ring Main (it's Friday and that's going to annoy quite a few people) or a Radial.


Yes spoon, they are wired with 2.5 pvc single and I always thought that would be the maximum rating, do you think I'm wrong?
I have wired those rooms with two feeds. The plan is to have two circuits with 4 socket or a ring of 8

Thanks
 
Last edited by a moderator:
So are you going with the 'maximum rating' or 20A??

Yes spoon, they are wired with 2.5 pvc single and I always thought that would be the maximum rating, do you think I'm wrong?

Either a Ring Main (it's Friday and that's going to annoy quite a few people) or a Radial.

I have wired those rooms with two feeds. The plan is to have two circuits with 4 socket or a ring of 8

Thanks
 
You cannot be guessing the circuit design and then ask people on a forum who have no knowledge of the site to confirm your guesses are correct.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Email
Joined
Time zone
Last seen

Thread Information

Title
Choosing a power supply, switch fuse size
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
83

Advert

Thread statistics

Created
Yanu,
Last reply from
ruston,
Replies
83
Views
8,330

Advert