If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
I am continuing my practising today and am trying to get 2 x 2.5mm into oval conduit. It's not as easy as I thought it would be.

First of all I used some old cable that I had all twisted up ready to be scrapped. No way was this going to go through either the 20mm or the 25mm conduit.

I then tried some new cable so that it wasn't all bent up. This went in fairly well to both 20mm and 25mm, no real difference, but it did take some force at one or 2 points to get it through a 2m length. The whole idea is for me to speed up on a rewire, so I'm just looking for tips for getting the cable through the conduit?

1. Lubrication?
2. 20mm or 25mm?
3. Completely unbent cable?
4. Do different manufacturers have oval conduits with different internal dimensions, or are they pretty much the same?
5. Both cables in at the same time, or one at a time?

Also, I can see how oval conduit helps speed things up if you have one or 2 cables in the drop, but what if it's 3+ cables? Do you then just use a second piece of conduit, larger conduit or go back to capping? If you use a second piece of conduit isn't that going to take longer than one piece of capping?

Wouldn't a piece of trunking be a good idea in a chase? Easy and quick to screw into the chase with concrete screws and you can use 32x16mm trunking if you have lots of cables?

Cheers guys. Back to work on Thursday, so all my practise threads will stop then! ?
 
  • Like
Reactions: Dave OCD
I am continuing my practising today and am trying to get 2 x 2.5mm into oval conduit. It's not as easy as I thought it would be.

First of all I used some old cable that I had all twisted up ready to be scrapped. No way was this going to go through either the 20mm or the 25mm conduit.

I then tried some new cable so that it wasn't all bent up. This went in fairly well to both 20mm and 25mm, no real difference, but it did take some force at one or 2 points to get it through a 2m length. The whole idea is for me to speed up on a rewire, so I'm just looking for tips for getting the cable through the conduit?

1. Lubrication?
2. 20mm or 25mm?
3. Completely unbent cable?
4. Do different manufacturers have oval conduits with different internal dimensions, or are they pretty much the same?
5. Both cables in at the same time, or one at a time?

Also, I can see how oval conduit helps speed things up if you have one or 2 cables in the drop, but what if it's 3+ cables? Do you then just use a second piece of conduit, larger conduit or go back to capping? If you use a second piece of conduit isn't that going to take longer than one piece of capping?

Wouldn't a piece of trunking be a good idea in a chase? Easy and quick to screw into the chase with concrete screws and you can use 32x16mm trunking if you have lots of cables?

Cheers guys. Back to work on Thursday, so all my practise threads will stop then! ?
@happyhippydad yes on the lubricant, yes on the wire being straight, when you say 2 mm or 2.5 mm I would have to say 2.5 mm and pull your cables in at the same time. I also pull a string in each conduit in case I missed something or need it for the future. Have a great day my friend
 
Not all the answers, but like @Megawatt yes to lube. Fairy liquid is good enough.
All cables in together, the friction of one cable to another is much greater than cable to the inside wall of conduit.

Push through a draw string first.... cable rods, a length of 6491x or something, and another pair of hands, One pulling, one feeding ....

If all else fails, strip off the outer sheath off t&e.
I didn’t just say that :o
 
Doesn't Appendix E of the OSG apply to this? if it does then is not the conduit too small?
 
Have not done the calculations, but is T&E outside dims larger than three single cores, they may be easier to pull through, although may make the work time longer.

Ohhh just thought two live, two neutral and one earth, much reduced c/c. ?
 
Doesn't Appendix E of the OSG apply to this? if it does then is not the conduit too small?
You love your appendix E Mike! ?
Using singles just isn't going to happen in a domestic situation, it would be great for conduit down the walls but an absolute nightmare to run the rest of it in conduit under floorboards etc.
 
It's not that difficult. ?
 

Attachments

  • Electrical - 1 of 1 (1).jpeg
    Electrical - 1 of 1 (1).jpeg
    165 KB · Views: 209
You love your appendix E Mike! ?
Using singles just isn't going to happen in a domestic situation, it would be great for conduit down the walls but an absolute nightmare to run the rest of it in conduit under floorboards etc.
I think he was jesting, at least I hope he was!! Not Been indicated what size oval conduit has it?
 
  • Like
Reactions: Megawatt
Who me jesting never, whatever makes you think that.
 
  • Optimistic
Reactions: DPG
Why I stopped using oval! In the pros -v- cons game, by the time you've threaded the stuff, sat it back in the channel, realised it's a couple of mm too long...... could have done three lots of capping.
 
  • Winner
Reactions: sajeel
easy to get 2 x 2.5's down a 25mm oval. and the propritry clips drilled and fixed saves bashing your fingers, or mortar crumbling when nailing capping.
 
Do you need 2 x 2.5’s? Just spur one socket off the other.
 
Lubrication definitely helps I find - in multiple situations!

ae235

This is the proper stuff, though washing up liquid works too - Can still be frustrating though gripping the end when it does come out - probably same for the cable too....?

But cheap oval conduit from Screwfix is a pig to work with I find and bends/crimps itself if not treated with care. Might be worth trying other makes from a wholesaler.
 
So.....

How about when you've got 3+ cables, what do you guys use? I guess the vast majority of chases have 1 or 2 cables and will fit into oval, so when you do have 3+ cables you just use capping? Or perhaps larger oval?
 
Two lengths of oval in a wider chase?
 
If your having problems getting cable into conduit -the conduit is too small. Start thinking of other ways around using 2 x 2.5, as suggested make it a spur? reduce cable size along with MCB rating? Or chase out a bit more.
 
2x 2.5t&e in a 25mm oval should be a breeze over 2m but using shorter lengths sometimes makes life easier.
The key is keeping them straight!
 
  • Like
Reactions: HappyHippyDad
The art is to keep them straight like off the drum push them down together when it gets tight bash the oval tube against the wall whilst pushing, obviously as the length gets longer you have to stand on steps.
 
2 x 2.5 easy fits a 20mm oval if both cables are feed through flat

3 x 2.5 easy fits a 25mm oval again cables need to be pushed through flat
 
Pushed through???? don't any of you use a draw tape?
 
  • Like
Reactions: ruston
We might not be the smartest people over here, but there's a good reason why our electricians use round conduit for the majority of domestic installations.

It's not expensive, so why not deepen that chase and see the advantages first hand?
 
If it makes it easier why not? banging the conduit against a wall and standing on steps does not sound like a 2m length.
 
  • Like
Reactions: Dave OCD
7029 dave my reply was to a previous post that questioned using a draw tape.
 
No need for a draw tape. 2x 2.5mm2 t&e goes in 25mm oval extremely easily in my experience. Cut it to the correct length and push cables through should take 30 seconds or so. Probably including pushing the conduit back into the chase and cables into box.
 
If it makes it easier why not? banging the conduit against a wall and standing on steps does not sound like a 2m length.
Yes... but he's only 4'8" !
 
Yes... but he's only 4'8" !
Use shorter lengths of conduit, say for a 6 ft run use 3x 3ft pieces, you will never rewire in PVC conduit at that sort of length so a joint wont hinder you in any way.
 
Use shorter lengths of conduit, say for a 6 ft run use 3x 3ft pieces, you will never rewire in PVC conduit at that sort of length so a joint wont hinder you in any way.
I have managed to yank twin & earth cable down existing oval conduit...
 
  • Agree
Reactions: AJshep
33 posts on sliding some cables into a tube.
 
  • Funny
  • Like
Reactions: DPG and westward10
  • Like
Reactions: nicebutdim
Having never used oval tube, just capping, I can't really see the appeal? What's the advantage, sounds like a hassle.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

HappyHippyDad

Esteemed
Arms
Supporter
~
Joined
Location
Gloucestershire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Getting 2 x 2.5mm into oval conduit?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
39

Advert

Thread statistics

Created
HappyHippyDad,
Last reply from
Mike Johnson,
Replies
39
Views
17,672

Advert