The "Loop Length" column shows the cable length from CU to first light switch (P1) and between each light switch thereafter.
I think you are describing the method shown in the Example below.
View attachment 119067
Yes

I did follow this through and as you say the drops appear significantly lower.
I'd dismissed it believing the values couldn't be that far off from the standard forumla used in methods 1 & 2.
Provided I haven't mucked up on the arithmetic, the max Vd is 1.65V (0.72%) which I'm struggling to believe, but happy to be schooled.

View attachment 119068
I haven't checked any numbers, especially working on small phone screen, but the approach looks right.
 
Its been an interesting excercise that I think has highlighted its not neccassarily the furthest point you'd find the greatest Vd as some have suggested. In this circuit Vd appears to be at its worst 45m from the CU whereas the furthest point is 51.5m.

The question I suppose I'm asking myself at this point is why isn't it always calculated in this detail?
Is it simply time where the alternative is a playing it safe approach with a quick calculation that could result in either an oversized cable or split circuits.
 
I’d need to stick my head in a theory book as a quick refresher but it occurs to me that what’s also missing from this discussion (as, if we’re going to have an actual theory discussion on here for a rare refreshing change then let’s have one…) is that the entire load on this circuit/s is LED and therefore all manner of other aspects come into play (theoretically) as well to affect the energy consumption - inrush and reactance / pf being two obvious ones. Add to that mix some good old fashioned conductor induced voltages from a few 2-way strappers and some smatterings of capacitance and the smoke starts coming out of your ears. The standard circuit maths is otherwise straight forward if not tedious as it’s resistances in parallel for every combination of Sum(lb) radial line (plus the feeders in every combination).

(This ^^ is why we have prescribed tables to use instead, stops the ear smoke thing).
 
  • Agree
Reactions: Simon47
Has it already been mentioned that in some lighting configurations, the line takes a much longer route than the neutral….?
Do you take an average, or the maximum?

Especially long corridors with a couple of 2 ways and any number of intermediates inbetween.


My 2 pennies worth is that the tabulated values have all these thoughts already built into them…
 
  • Like
Reactions: Watkins88
The question I suppose I'm asking myself at this point is why isn't it always calculated in this detail?
I created a voltage drop spreadsheet for this sort of thing. I used to use it to calculate the drop when designing regular 230V lighting circuits for ordinary houses, but I don't bother anymore. After using it a few times, I concluded that with LED lighting, it's not easy to exceed the 3% allowance, and even if you did go over by a little way, the consequences are negligible.
 
  • Like
  • Winner
Reactions: DPG and Simon47

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
Didcot
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Other
If other, please explain
.

Thread Information

Title
Voltage Drop Calculation vs OSG
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
24

Advert

Thread statistics

Created
Watkins88,
Last reply from
Pretty Mouth,
Replies
24
Views
2,084

Advert