Hi guys,

I would just like to ask if any one could look at my test procedure off the top of my head and give any advice or pointers or whether its too long winded or short. got an exam in 2 weeks so trying to drill it in to this thick skull :)
Many thanks

Safe Isolation has been carried out:



  • Seek permision , Inform client and relevant persons that test is about to be carried out
  • Make area safe by putting up barriers and warning notices
  • Disconnect lamps and link out or disconnect other sensitive devices that may be vulnerable to test voltages
  • Select an insulation resistance tester, Check tester is calibrated, leads show no sign of damage, and that tester is functioning.
  • Select the Megaohm range set at 500V DC
  • Identify circuit to be tested, and test between Live - Neutral and record result. Do the same test between Live - Cpc and Neutral - Cpc record results.
  • Expected result a minimum of 2 M/ohm.
  • Reinstate circuit
 
you have not mentioned safe isolation and lock off. that should be your 2nd bullet point. ... prove volage tester, isolate, prove dead... before you connect IR tester.
 
  • Like
Reactions: 2 people
Megohms not megaohms, your terminology is very important mate. Everything you need to know is in GN3 so stick your head in that and only come up for air.
 
  • Like
Reactions: 1 person
you have not mentioned safe isolation and lock off. that should be your 2nd bullet point. ... prove volage tester, isolate, prove dead... before you connect IR tester.
Thanks for response telectrix I stated that safe isolation has been carried out in the scenario :)
 
Megohms not megaohms, your terminology is very important mate. Everything you need to know is in GN3 so stick your head in that and only come up for air.
Thanks trev i would have stumbled onsome basic stuff there nice one :)
 
I agree trev. do you think it would be ok in the exam to state:
I would first test at 250V then test at 500V or would they prefer the setting of 500V
 
a continuity test L-N could be done first to ascertain if any loads are still in circuit. then a 250V, finally a 500V. and if a plumber or plasterer is working in the vicinity, give it 1000V. LOL.
 
  • Like
Reactions: 5 people
a continuity test L-N could be done first to ascertain if any loads are still in circuit. then a 250V, finally a 500V. and if a plumber or plasterer is working in the vicinity, give it 1000V. LOL.
Lol i feel sorry for any apprentice of yours :)
 
wasn't that paul m?
 
I was talking about this fella http://m.youtube.com/results?q=megger%20ears#/watch?v=8whQKK4Q-u8
 
sounds like a good idea for an alarm clock.
 
We found a dog training collar for nuisance barking that consisted of a microphone and 2 probes built into a collar. Decided it looked a bit dodgy for the mutts but stepson decided we were too soft, strapped it rouond his neck and started barking. Funniest thing I've seen when the collar zapped him and he went down like a sack of spuds and lay twitching on the living room carpet. Must have the zap-ability of a taser! So glad we didn't try it on the dogs first lol!
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Advice on insulation resistance test procedure :)
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
22

Advert

Thread statistics

Created
LittleHelper,
Last reply from
PEG,
Replies
22
Views
3,628

Advert