iamelectric

got a job to install a 63amp supply 3 phase commando socket , for a lighting show for an opening night , it was a metre from the D.B so i wired it in 16mm SY cable, i have now been asked to supply am extension cable for it , one male plug one female plug , about 25m long , i was thinking of using 10mm SY for it as its more manageable , but 10mm comes in at 61 amps ccc , is this ok as its an extension?
 
Personally I'd use H07RNF 16mm cable. 16mm to allow for any high neutral currents from the dimming equipment and to reduce voltage drop.
 
got a job to install a 63amp supply 3 phase commando socket , for a lighting show for an opening night , it was a metre from the D.B so i wired it in 16mm SY cable, i have now been asked to supply am extension cable for it , one male plug one female plug , about 25m long , i was thinking of using 10mm SY for it as its more manageable , but 10mm comes in at 61 amps ccc , is this ok as its an extension?

Why would you think that an extension lead can have a lower ccc than the OCPD protecting it?
 
well its like plugin a machine in that only has a 1.5 cable into a 32amp circuit
 
^^^^ what do u mean i have already installed the socket
As in the 63A socket (and plug) of the extension cable you are creating?

In any case a different sort of regulations apply ... BS7909 and regulation 7.3.3 states:

Cables for use outdoors and in general use should be rubber insulated and
sheathed in accordance with BS 7919 (H07RN-F or equivalent), with a
voltage designation of not less than 450/750 V (heavy duty flexible, as
defined in BS 7540-1) and resistant to abrasion and water.

NOTE 2 Thermoplastic cables are not designed for use outdoors. For example,
cables known as ‘arctic blue’, ‘SY’ are thermoplastic and are not suitable for use
outdoors.
 
what i mean to say is the current demand from any applied load should not exceed the rating of the cable attached to it...
 
got a job to install a 63amp supply 3 phase commando socket , for a lighting show for an opening night , it was a metre from the D.B so i wired it in 16mm SY cable, i have now been asked to supply am extension cable for it , one male plug one female plug , about 25m long , i was thinking of using 10mm SY for it as its more manageable , but 10mm comes in at 61 amps ccc , is this ok as its an extension?
16mm 3 core H07-RNF ... nice n easy :)
 
a commando plug does not have a fuse in it , i have seen many extensions and machines plugged into 32amp circuits without being fused down
 
well its like plugin a machine in that only has a 1.5 cable into a 32amp circuit

Would you use a 5A extension cable to power a 10A appliance, fed from a standard ringmain? Daz
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
63amp extension lead
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
27

Advert

Thread statistics

Created
iamelectric,
Last reply from
iamelectric,
Replies
27
Views
3,770

Advert