hi,
I did Ze test, I got 0.22 ohms but PFC test I got 22 Amps. it is very low. I am expecting a (230/0.22=1045 amp ) by theory
So pls let me why it is very low reading
Picked up my tickets yesterday, shirt ironed, car fueled up and WE ARE OFF TO WEMBLEY :willy_nilly:
Should be a great game and maybe a modern day classic. Both teams will give it 100% just to have the bragging rights within our local area, Cas fans will be drowning their sorrows tonight though...
Thought I had posted this back in Jan, but looks like it didnt post.
A meter reader turned up unannounced to take a reading/inspection of the PV installation at my setting, said this was normal and would happen every 2yrs !
danesol
Thread
check
inspection
meter
meter readingreading
system
turned
hi
I was on a job testing incoming supply on a TT systems the earth loop reading was 2,53ohms now what my question is
It was a 2 commer 53 i am guesting that means 2.53ohms if you test result are lower you get 0.12 (point )why does it change to a commer or am i reading it wrong
Hi everyone, I have my 2394 practical coming up soon and wanted to know if you can do a global insulation resistance test rather than individual circuits and if the assessor would be happy with this, just thinking it would save a lot of time when carrying out all your tests.
Hi.
I have have tested a property with a TN-s system and the main ze reading is 2.98 ohms which is far to high for a TN-s system which needs to be within 0.8. What would be should be done in this situation? Contact electric board?
Thanks.
Hello Gents,
I have a low IR reading on a lighting circuit - the circuit is 50 years old - i believe the fault is at the pot connection as there has been a downpour of water on this connection - I was going strip back the sheath and identify the point where the IR reading...
Isn't it ok to join the live and neutral together and test down to earth? I did this today on 250 volts as there are dimmers on the circuit and lv lights and a smoke detector. Having done this I got readings of somewhere around 1.6 m ohms. I left that circuit as it is not urgent to finish it yet...
Hi scratching my head alittle today as of why when I test between two different circuit I was getting 55 meg ohms on L and N and 1700ohm on E.
It is a horse stables and I can see one cable goto the the right hand side stables and the other stays in the left side stables, I thought it might...
Jimmyb
Thread
between
circuit
circuits
different
insulation
reading
right
test
Hi guys job today for nuisance rcd tripping ,I thought it was an appliance as I explained in a post yesterday but turns out it wasn't . Anyway disconnected the only neon I could see , unplugged everything run an IR test ,great neutral to earth but earth to live 0.02 . Checked every socket , I...
hi everyone , this is my first time on this forum , anyway this is my story why I am here writting to you ,
6 month ago my mother and father in-law wanted to change the lighting in the new house they bought and they find a set of light from homebase they really like , because they was eco...
Hi All,
Just returned from trying to locate an issue with an upstairs lighting circuit -
with the circuit L/N/E disconnected from the board and breaker I get he following readings:-
(a) Type 2 Insulation Resistance Test = 49.7 taken at 250V
(b) Voltage reading on the (dead) circuit of 3.5V...
chloebear
Thread
checking
circuit
induced
lighting
lighting circuit
problem
reading
voltage
Does anyone else have problems with there continuity readings my readings never seem to be stable for example a newly installed ring end to end resistance on neutral and line ill get .46 and then a reading of .04 on line end to end the leads are always nulled and I even check readings on calcard...
hi, just after some advice regarding a megger 1502 that reads 1v on start up. could this just be a calibration issue (last calibration 11 months ago) or a possible fault. battery good 12.2v. many thanks. j
Hi . have a quick question, hope you can help me with
A recent EICR found (amongst some other things ) that I have no mains bonding on the water supply.
I have a stopcock at the end of the drive, but have never been able to locate an internal one (there was an extension built and short off...
Hi I was wondering if any one can help me. I've done a R1 and R2 reading on a lighting circuit and there is a high reading in the middle of the circuit. I would usually expect the highest reading at the end of line. Does any one know why this is happening thanks
Guys, request advice.
I was recently carrying out remedial work on 2x Ltg cts reported on EICR as having very high Zs value.
When I retested the measured Zs was 44.8 and 42.6. These are on a TNC-S system and Crabtree C50 5a MCBs. These would appear to be readings expected of a TT System!
I...