volt drop

In electronics, voltage drop is the decrease of electric potential along the path of a current flowing in a circuit. Voltage drops in the internal resistance of the source, across conductors, across contacts, and across connectors are undesirable because some of the energy supplied is dissipated. The voltage drop across the load is proportional to the power available to be converted in that load to some other useful form of energy.
For example, an electric space heater may have a resistance of ten ohms, and the wires that supply it may have a resistance of 0.2 ohms, about 2% of the total circuit resistance. This means that approximately 2% of the supplied voltage is lost in the wire itself. An excessive voltage drop may result in the unsatisfactory performance of a space heater and overheating of the wires and connections.
National and local electrical codes may set guidelines for the maximum voltage drop allowed in electrical wiring to ensure efficiency of distribution and proper operation of electrical equipment. The maximum permitted voltage drop varies from one country to another. In electronic design and power transmission, various techniques are employed to compensate for the effect of voltage drop on long circuits or where voltage levels must be accurately maintained. The simplest way to reduce voltage drop is to increase the diameter of the conductor between the source and the load, which lowers the overall resistance. In power distribution systems, a given amount of power can be transmitted with less voltage drop if a higher voltage is used. More sophisticated techniques use active elements to compensate for excessive voltage drop.

View More On Wikipedia.org
  1. L

    Volt drop question

    Hi I've got a question regarding volt drop. When calculating volt drop to a 3 phase distribution board do I use 230v (11.5v) or 400v (20v) The board I'm attempting to put a cable to is 75 meters away. Design current 100A From TABLE 4D4A Cable selected = 25 mm² For 25 mm²: mV/A/m 1.75 for 230v...
  2. N

    Solar PV volt drop and cable sizing.

    Morning gents, just a quick one. I've posted this already on the Solar PV forum but thought I'd add it here too as VD and cable calcs are always a good topic of discussion. So I have a Solar PV system to install this weekend, its a 10KW single phase system on a farm. I'm going to be running a...
  3. D

    working out volt drop

    Hi I have been looking in to wiring up a garage which has a exsiting swa cable running to it just wanted to run this by some of your for your opinion . Supply is from 20a rcbo using 3 core 2.5mm swa into isolator In the garage there is to be 2 power sockets and 1 lighting circuit with 4...
  4. driverman

    Volt drop calcs on ring main

    Hi Guys, I'm not into design etc and never have been really but how do you calculate volt drop on a distribution ring main circuit? Ring circuit say covering a large area supplying various loads/buildings. I was thinking split the ring and work it out as 2 x radial circuits, but 1 radial may...
  5. M

    Volt drop

    Hi, Im a fairly new sparky, So just wanted to get a little idea as im not 100% sure, Im adding 12m of 1.5mm cable in trunking into a conservatory from a fcu of the ring main the volt drop for this part would be 4.5v so i may need to up the cable size. But what i need to know or confirm is what...
  6. M

    volt drop query

    Hi all, Am wiring in some lights in a carpark.. The total distance is 150m there are 4 lighting posts rated as follows A-200w B-300W C-300W D200W (with A closest to CU) All loads are LED They are spread at distances of CU - A = 30m A-B = 40m B-C = 40m C-D = 40m Having done my volt drop calcs...
  7. S

    Volt drop to summer house heating

    Hi. First time poster here so please go easy on me. A customer of mine has had a summer house built at the rear of her garden which has been supplied with two 6Kw heaters! Yep, 12Kw!! She would also like 2 switched double sockets and about 4 LED spots installed. Now the problem, as if a 12Kw...
  8. P

    Volt drop question

    Hi everyone, I am intending on working in the uk shortly, i am from ireland and dont have the uk regs presently. I am trying to prepare for the exmas i will face and the cable calculations/volt drop calculations are something i cannot remember doing here in ireland in my college time so my...
  9. K

    Volt drop at the other end of a SUB main.

    Hello people Just so i get this right i thought i would post my maths here for people to comment on. Garden lights on a sub main. Sub main is 20meters from the main CU on a 6mm armoured cable. the last light is 50 meters from the sub main. meaning end to end 70 odd meters. So my maths are...
  10. Simonslimline

    3phase volt drop.

    This is one of a weekly question by sparks magazine posted on Facebook to win free tools each week. Everyone has answered B. 8Volts. I am not sure this is correct. Please could anyone help me with this. I have posted it up in here rather than just the trainee section so more people will see it...
  11. O

    Volt drop question

    Hi all Just had an enquiry for 50 kw ground mounted PV system, the proposed system is to be connected to a three phase supply In an industrial unit, the ground mounted array will be approx. 200mtrs away from the unit. The inverters and generation meters are to be mounted next to the...
  12. A

    Volt drop tables for LSF T&E

    Which table do you use in BS7671 for volt drop for LSF Twin and Earth? There does not appear to be a table for LSF cable. 4D5 refers to the grey PVC cable and is not the right one to use for the white LSF. Any help would be appreciated.
  13. H

    Volt Drop

    Good Morning Visited a property yesterday. Customer saying only certain appliances working from double socket in bedroom. Electric toothbrush yes, vacuum cleaner no. After inspecting socket and wiring find that the socket has been taken as a spur from downstairs lighting circuit on 6A MCB...
  14. A

    Volt drop on outside lighting

    I got called to a job this afternoon, it's outside lighting, about a 1000w of lamps on the whole circuit, and when trying to quote for it done a few calcs and the volts drop is massive, it's 24 volts, the circuit is run in 3 core 4mm swa, and is 300m in length, now I know that it's well over the...
  15. M

    3 phase volt drop.

    Howdy, when designing a 250A 3 phase supply, what column value do you use for volt drop?? Table 4d4b, section 4(3/4 core 3 phase ac) column r,x or z. I'm thinking r, but not 100% sure. Cheers in advance!!!
  16. J

    Volt drop and load

    Hi. I am new to the forum and most of my experience is in 12/24v systems. I have a bit of a basic question really and was hoping to clear it up. If I had one PSU with an output voltage of exactly 12 volts and 4 loads of 1 amp each and a 5th load of 2 amps all ran in 1 mm cable and each cable run...
  17. S

    Volt drop question

    Hi guys could do with a little advise on a rather large job re-wiring lamp posts in a car park. The supply will need to cover a distance of around 120M from mains to sub board where floods are already wired in 2.5mm SWA on 2 circuits the furthest travelling another 123M the other travelling...
  18. M

    mixed 1.5 and 2.5 mm lighting - volt drop calcs

    ok.. so any help appreciated..i want to add some Klik lighting management boxes to the end of a circuit to control 10 lights. The circuit up to the ceiling rose I wish to utilise to feed my first klik is wired in conduit using 2.5mm cable. I want to add a two way lighting switch to control the...
  19. jackhammerJIM

    volt drop calcs and 230 v

    why do we have to do the calcs to 230v when the supply never is 230v measured voltage at source is 248 volts at the site i am on at the moment , can somebody shed some logic on the idea before i start engineering an 18 volt drop into my cable sizes ( a joke of course but why not ? ) :ihih:
  20. G

    volt drop on elv LED wiring

    Hi. I'm new to LED wiring and am wondering how to work out volt drop when using 24 volt drivers and 2mm elv cable. The length of run is about 20 metres. I've read that the 4% stays the same as 230v but what would be the maximum length of cable that could be used?

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock