danjordan
UK
United Kingdom
Hi, I have a question regarding electrical connections. I currently have a 13A oven that is below 3kw so is plugged in using a normal 13A plug. I want to add an 13A induction hob which is also a normal 13A plug. Is it acceptable to spur a single socket from the oven socket and plug the hob into that? Or does it have to be totally separate?
Yes with the following considerations
1. The exiting socket must not already be a spur. (assuming circuit is a ring)
2. Be mindful of the loading on the circuit, it should be fine if you have a separate ring circuit for the kitchen. But Washing machine, Dishwasher, Drier, Kettle, Fridge, Toaster etc etc. Most Kitchens have a dedicated circuit for the cooker which reduces the burden on the ring circuit.
Hi, the oven plug socket is on the same circuit as a couple of other kitchen plugs. Presumably adding a 2.7kw induction hob would cause this to overload if the job and oven were on at the same time?
I have a spare MCB in the CU, would the best option here to run 6mm2 cable from the 32A breaker down to a dual outlet plate and go into two separate single sockets?
Yes, that would be the better way.
UK
United Kingdom
13A Induction Hob and 13A oven
DIY Electrical Advice
Thread Tags
danjordan,
mainline,